I came across this article on the "Fluke" website. It's great reading and it just might save someone's life.
Top 3 solar PV safety hazards and how to avoid them
07-31-2019 | Renewable energy
Although much of the public may think radiation from the sun is magically transformed into electricity that powers all types of equipment and devices, solar technicians know there is much more to it.
In PV, current is "wild" and not limited by electronics, which has implications for hidden ground faults, wire sizing, and is the impetus for rapid shutdown. The control measures and best practices to mitigate risks will differ when working with PV versus any other kind of energy generating resource.
Here are three of the most common electrical hazards with PV systems along with specific control measures you can take to reduce their risk.
Hazard 1. Shock or electrocution from energized conductors
Just as with other electric power generation, PV systems present the risk of shock and electrocution when current takes an unintended path through a human body. Current as low as 75 milliamps (mA) across the heart is lethal. The human body has a resistance of about 600 ohms. Per Ohm’s law, voltage (V) equals current (I) times resistance (R), so V = IR.
To calculate the amount of current that would course through a person’s body if exposed to 120 V, simply divide 120 V by 600 ohms (I = V/R), which totals 0.2 amps or 200 mA. That’s more than 2.5 times the lethal limit of 75 mA, so protecting yourself and your workers against such an event is critical.
Electrical shocks are typically caused by a short circuit resulting from corroded cables and connections, loose wiring, and improper grounding. Key places to look for these conditions in a PV system include the combiner box, PV source and output circuit conductors, and the equipment grounding conductor. The grounding conductor bonds all metallic components together—and eventually to ground—through the grounding electrode conductor and grounding electrode.
Control measures: Rapid shutdown systems
Energy produced from PV string systems varies directly with the sun. To reduce shock hazard for technicians and first responders, we need a way to shut those strings off during a short circuit or power outage. The 2017 National Electrical Code (NEC), Section 690.12 requires the “rapid shutdown” of PV systems both inside and outside the PV array boundary. According to section 690.2 of that code, PV array boundary is a mechanically integrated assembly of modules or panels with a support structure and foundation, tracker, and other components, that form a DC or AC producing unit. This includes controlled conductors located inside the boundary or up to three feet from the point where they penetrate the surface of the building.
As of 2019, the NEC made these requirements more stringent by requiring:
In addition, many jurisdictions in the U.S. require that rooftop PV arrays have setbacks that allow firefighters to access the system. For instance, the California Residential Fire Code requires PV modules be at least three feet from the ridge of the roof.
Hazard 2. Arc faults that spark fires
As with any electrical system, fire is always a potential hazard. Perhaps one of the most common causes is electrical arc faults, which are high power discharges of electricity between two or more conductors. The heat caused by this discharge can cause the wire insulation to deteriorate and thus cause a spark or “arc” that causes a fire.
PV systems are subject to both series arc faults caused by a disruption in continuity of a conductor, or parallel arc faults caused by unintended current between two conductors, often due to a ground fault.
Control measures: Arc-fault circuit interrupters
An arc fault may lead to a short circuit or ground-fault, but it may not be strong enough to trigger a circuit breaker or a ground fault circuit interrupter (GFCI). To protect against arc faults, you need to install an arc-fault circuit interrupter (AFCI) outlet or an AFCI circuit breaker. AFCIs detect low level hazardous arcing currents and shut off the circuit or outlet to reduce the chances of such an arc fault sparking an electrical fire.
The NEC Section 690.11 mandates that PV systems operating at 80 V DC or greater between any two conductors be protected by a listed PV AFCI or equivalent system component. The protection system needs to be able to detect arc faults resulting from a failure in the intended continuity of a conductor, connection module, or other component in the PV system DC circuits.
Hazard 3. Arc flash leading to explosions
Large-scale PV arrays with medium and high levels of voltage are susceptible to arc flash. This is especially true when a technician is checking for faults in energized combiner boxes where PV source circuits are combined in parallel to increase current, and when checking medium-to-high voltage switchgear and transformers. An arc flash releases hot gases and concentrated radiant energy up to four times the temperature of the sun’s surface—as high as 35,000° F (~19,500° C). It occurs when a large amount of energy is available to an arc fault, in both DC and AC conductors.
Arc flash is an issue for systems over 400 V so both residential inverters that typically have a maximum input voltage of 500 V and large-scale inverters that have a maximum of 1,500 V are at risk. Before the advent of large-scale solar energy systems, arc flash was solely considered an AC issue since DC voltage was limited to off-grid applications where batteries of less than 100 V were used. The National Fire Protection Association (NFPA) Standard 70E requires an arc flash hazard risk analysis be conducted and Personal Protective Equipment (PPE) used for DC systems over 100 V.
Control measures: AC and DC side mitigation
Arc flash mitigation in PV systems is divided by DC (before the inverter) and AC (after the inverter). DC-side mitigation for large solar arrays (100 kW +), is especially important at the combiner box where multiple strings of solar panels are combined in parallel to increase the current. To reduce the potential for arc flash, large-scale systems can use multiple string inverters that themselves can connect multiple strings in parallel, instead of using one or two large central inverters that require combiner boxes. AC-side mitigation includes arc resistant switchgear, which redirects arc flash energy through the top of the enclosure, away from personnel and equipment.
- Modules and exposed conductive parts within the PV array boundary to be reduced to 80 V within 30 seconds.
- Conductors located outside the array boundary to be limited to 30 V within 30 seconds.