Top-balancing Pytes V5 with Ecoworthy All In One?

How much energy can you get from them before low voltage shut down.
Well, I've not run it to low voltage shutdown yet. The lowest I've hit was 9% while provoking the inverter to see the reaction to 15% and 10% points. It's good to know that the alarms/cutoffs work while you're stood watching and able to do something about it.

It's also good to know that at 10% -- when the inverter gives up and throws over to bypass -- that if the grid goes away, it comes BACK onto battery despite being "low" and carries on down to the next trip point (5% last-gasp) at which point I assume it's lights out. I didn't go there...

From early testing/notes, using change-in-SOC over time while discharging, it came out around 9.8-9.9kWh which was close enough to theoretical 10.24kWh to be satisfied the batteries were ok.

This is subject to measurement error (the load not being 100% constant over time) and 0-100% SOC not necessarily being the true size of the pack at that stage (high point/low point not fully found) and so if I repeated it, I expect a larger capacity.
 