Hello,
I'm looking to set up stationary panels for an Ecoflow Delta Pro in Southern California. I'm hoping to cycle it as much as possible.
This is my plan:
6x of these used REC panels set up 3s2p. I believe that gets me:
(260x6) = 1560W -- staying under the 1600W max input
(37.8x3) = 113.4 VOC -- staying under the 150V max input
(1560/113.4) = 13.76Amps -- staying under the 15A max input
Question #1 Am I calculating that right?
Question #2 -- The Delta Pro might have to be 40 feet away from the panels. I was planning on using the 8-AWG cable recommended by Will. I'm getting confused looking at the DC wiring chart. Do I need 6-AWG cable? Does the total run include both positive and negative (is it really 80 feet, requiring 4-AWG?)
Question #3 -- Should I add OCPD fuses?
Thanks in advance for the help!
Dan
I'm looking to set up stationary panels for an Ecoflow Delta Pro in Southern California. I'm hoping to cycle it as much as possible.
This is my plan:
6x of these used REC panels set up 3s2p. I believe that gets me:
(260x6) = 1560W -- staying under the 1600W max input
(37.8x3) = 113.4 VOC -- staying under the 150V max input
(1560/113.4) = 13.76Amps -- staying under the 15A max input
Question #1 Am I calculating that right?
Question #2 -- The Delta Pro might have to be 40 feet away from the panels. I was planning on using the 8-AWG cable recommended by Will. I'm getting confused looking at the DC wiring chart. Do I need 6-AWG cable? Does the total run include both positive and negative (is it really 80 feet, requiring 4-AWG?)