I have a Solis RAI-3K-48ES-5G AC Coupled Inverter and 3 Fogstar 5.12kWh rack batteries, the Pace BMS in these is set to mimic Pylontec as Fogstar isnt on the Solis list and that seems to be working out just fine.
My problem is 2 of the rack batteries will charge and discharge in sync with each other in percentage terms read from either the batteries screen or from the BMS via PbmsTools V2.5FN. The current discharge and charge remain pretty close to the same on these 2 batteries too when viewed via PbmsTols.
Battery 3 though seems to have a mind of its own, generally lagging behind the other 2 by up to 5% in charging and not taking the same charge current as the other 2.
Even if I charge all 3 together to 100% via solar during the day, by next morning they will be 71%, 71% & 67% As you can see B1 & 2 are still in sync 12hrs later but B3 is way off at 67%.
The 3 batteries are in parallel with pos/neg supply cables to opposite ends as in photo. I have tried various other combinations starting with red to battery 3 and black to battery 1, both supply leads to battery 2 and also both to battery 3 with pretty much the same results. Battery 3 always goes out of sync with the other 2 remaining in sync.
This lead me to the conclusion that B3 had a problem so I swopped it for another battery, within 24hrs the replacement B3 is again out of sync.
I tried a constant 39A charge from the Solis.
B1 registered 12.01A 54.10v 70% on PbmsTools
B2 registered 11.64A 54.08v 69%
B3 registered 15.16A 54.03v 71%
Why would B3 get the lions share of charge current? I thought they should be balanced at around 13A each.
So does anyone have any ideas as to how I get the 3 batteries to act as one or close to same?
Anyone here also using multiple Fogstar 5.12kWh server rack batteries? Your experiences may help.
My problem is 2 of the rack batteries will charge and discharge in sync with each other in percentage terms read from either the batteries screen or from the BMS via PbmsTools V2.5FN. The current discharge and charge remain pretty close to the same on these 2 batteries too when viewed via PbmsTols.
Battery 3 though seems to have a mind of its own, generally lagging behind the other 2 by up to 5% in charging and not taking the same charge current as the other 2.
Even if I charge all 3 together to 100% via solar during the day, by next morning they will be 71%, 71% & 67% As you can see B1 & 2 are still in sync 12hrs later but B3 is way off at 67%.
The 3 batteries are in parallel with pos/neg supply cables to opposite ends as in photo. I have tried various other combinations starting with red to battery 3 and black to battery 1, both supply leads to battery 2 and also both to battery 3 with pretty much the same results. Battery 3 always goes out of sync with the other 2 remaining in sync.
This lead me to the conclusion that B3 had a problem so I swopped it for another battery, within 24hrs the replacement B3 is again out of sync.
I tried a constant 39A charge from the Solis.
B1 registered 12.01A 54.10v 70% on PbmsTools
B2 registered 11.64A 54.08v 69%
B3 registered 15.16A 54.03v 71%
Why would B3 get the lions share of charge current? I thought they should be balanced at around 13A each.
So does anyone have any ideas as to how I get the 3 batteries to act as one or close to same?
Anyone here also using multiple Fogstar 5.12kWh server rack batteries? Your experiences may help.