I tried to 'ground' the 60v middle tap of my Reliable and it instantly fried it!
Probably because you had a bond between neutral and earth elsewhere, and once you connected the center tap to earth, you essentially bonded its neutral to earth?
I tried to 'ground' the 60v middle tap of my Reliable and it instantly fried it!
You state ' by those capacitors is in the order hundreds of kiloOhm (big enough to make this safe to touch)'.actual impedance will be lower
Unless the inverter is neutral to earth bonded and a RCD is fitted, I cannot meet the UK regulations for a permanent install of an inverter in a mobile application.
Voltage is relative.I used to be an ABYC certified marine electrician about 20 years ago. I understand electricity fairly well, however I have not been able to find much online regarding portable inverters using 60 volts on opposing phases on both hot and neutral.
The inverters we used in boat installations never had this mode of operation.
The owners manual I have for the inverter says it is not suitable for feeding in to an electrical distribution panel and to not bond ground and neutral or damage to the inverter may occur.
Ok, all of this is fine. I can use this one simply to run an item directly.
My query is to try to understand how the ground works.
What happens if you plug in a device that has a ground fault in to one of these inverters with an energized case sending current down the ground wire to the inverter?
Does the inverter get fried and that is your failsafe?
Just trying to understand how the ground functions here.
To connect the ground in your device to system ground.I am still trying to understand what function the ground conductor has on these inverters.
Yes - I hooked the 60v middle tap to the house ground. The house ground runs to the main panel where it's bonded to the neutral (of 240v/120v US split-phase wiring).Probably because you had a bond between neutral and earth elsewhere, and once you connected the center tap to earth, you essentially bonded its neutral to earth?
You state ' by those capacitors is in the order hundreds of kiloOhm (big enough to make this safe to touch)'.
How can the actual impedance be lower? I can see leakage through EMI filters but the impedance would need to be in the region of 5k ohms.
Agreed, but any human contact will have series resistance. The UK specification domestic type A 30 mA RCD tend to trip at around 20 mA, design specification sets a no trip level, 50% of rating, to prevent nuisance tripping. I have not investigated how a RCD behaves without the neutral bond, something to look at. However second hand reports suggest the RCD will not operate.short the line or neutral to the center of those capacitors
but any human contact will have series resistance.