Alright, so, assuming everything EG4 has just had me do is only resetting the SOC calibration, and isn’t going to help my one cell that is much lower than the others during charging, what is my next step?
I’m running open loop, and I use Midnite Classics to charge. I have super limited ability to be home when it’s going to be going into absorb charge just due to my schedule.
Is there a simple tool/software I can utilize to help manage this? Anything straightforward and succinct would be incredibly appreciated.
You can download the BMS software here:
Discover the reliable and durable EG4 WallMount All Weather Battery, featuring IP65 outdoor rating, 10kW power delivery, and 8000 cycle life.
eg4electronics.com
Need an adapter like this 4ch "deluxe" one:
Buy Waveshare Industrial USB to 4Ch RS485 Converter, Multi Protection Circuits, Multi Systems Support, Aluminium Alloy Case, Wall-Mount & Rail-Mount Support: Desktop Barebones - Amazon.com ✓ FREE DELIVERY possible on eligible purchases
www.amazon.com
Run it on a computer and use chrome for remote operation.
Base on your info, I don't think you will be able to get this pack in balance since I think your low cell is likely somewhere around a 28Ahr deficit.
Here's why:
If spec sheet is accurate, the bms balancing is 120mA at 3.2V (calcs out to 27 Ohm resistor) so at say 3.5V, it'll balance at 131mA. 28,000mAh / 131mA= >213 hrs or 9 straight days of continuous balancing/micro charging, holding at least 1 cell initially for all that time (and eventually all 15 cells at 3.5V), to me that's severe overcharging.
IOW, you'll be charging the low cell at 131mA. Any faster and tgt V will be reached and charging stops, though the discharge resistors keep working so the charging incrementally stays on a wee-bit longer each time.. emphasize "wee-bit", lol... if you are able to charge at this rate, the balancing resistors are basically absorbing the pwr to the hi cells.
My 280ah EG4 wall mount in SOC mode with 6000xp stops bulk (100%) at ~53v and floats at ~52.6 rest off day. It has never once reached the specified charging specs in SOC mode. EG4 recommended putting in lead acid mode and bulk it to 58v and float at 54v for a week of cycles, didn't help. Had this set up for over a year, when I visit this off grid place I feel like the battery capacity is diminishing over time. Morning voltage seems to be lower now. But no way to remotely monitor all the individual cell voltages at the same time and the app max / min cell voltage makes no sense.
This is exactly what will happen if the charging V is st too high. There is no chance for the cells to balance. The delta increases with each cycle. your hi and lo cells starts to see more "1 way action" where the hi cell keeps hitting the highs and the lows keep hitting lows vs other cells leading to lopsided degradation.
Best is to take cover off and individually charge lo and at the same time dischg hi.
There's really nothing else we can do once it gets to that point if we want to use most of the capacity.
If taking cover off is 100% no go and no other recourse, set bulk to lowest pack V that drives the highest cell to 3.55V (there's a reason why I use 3.55V vs all others, but that's a longer discussion) with float that drives highest cell to 3.475 and use batts for 1-2 years and it should balance out if batts hit bulk V each/everyday.
@Zapper77 :
Edit to add... when we have large imbalances , hitting 100% soc means nothing... who cares about soc at this point.
For Eg4/LuxP AIOs, running under soc, they hard code in a do not run <10%. If yoour bats hit this level, it goes to ac charge (if GT) and nothing will stop it outside of shutting it down until it gets to 13% where it goes to standby, waiting on PV. All the while, loads are being fed from grid and you won't be able to use batts until they get up to 15% soc.. God forbid you are on one of those plans where it's >$.75/kWh when this happens .
So if you have a say 10% imbalance, when soc resets to 100, your bms thinks you have 280Ahr capacity when you really have onl 250Ah. So guess what happens at 20%.. yep, soc goes off a cliff to 10%, but maybe worst a cell goes UVP.