The voc of each 12v panel is 23.2 and isc 9.99 a .
The two strings reach the scc with a voltage of 92.80 and an isc of 19.98 a .
I would have available 2 300w panels with an almost equal isc, the 39.6 volts voc and a 9.93 A isc almost equal to the 12 v .
If I add these 2 panels one per string I would increase the voc to 132.40 volts that would be managed by a victron 150/45 smartsolar.
My question is:
132 v are still in the victor management margin or are they too many?
Is the configuration I want to do correct (5+5)?
I attach the characteristics of the 12 v 180 w and the 24 v 300 w panels