Hey Everyone!
I'm reaching out in regards to my Solar setup behaving not quite as expected after an upgrade was done.
Hoping to have to some like minds help me decipher where I may have made a wrong turn, or what I could do differently.
- - - - - - - - - - - - - - - - - -
Currently I have two Solar Arrays.
The Old:
5 - 100 watt, 12 volt, 5.72 amp Mono panels.
60A EPEver Tracer 6415AN MPPT Charge Controller
10 gauge solar wire.
Wired in Parallel (attached image for connection types).

The New:
5 - 200 watt, 12 volt, 10.75 amp Mono panels.
100A EPEver Tracer 10415AN MPPT Charge Controller
EPEver MT-50 Remote Meter
10 gauge solar wire.
Wired in Parallel (same connections types as original panels)

Battery Information:
4 - 12v 200ah Deep Cycle Sealed Lead Acid

Inverter Information:
1 - 4000w Giandel Heavy Duty Pure Sine Wave Power Inverter DC12V to AC120V


Wiring Information:
The Panels all run on the provided 10 gauge solar wire down to their respective MPPT charge controllers. The 100A mppt charge controller runs two 2/0 gauge wires to the battery bank from the controller. The 60A runs something smaller like a 6 gauge I believe.

The Batteries are all tied with 2/0 gauge battery wire, and the last wired battery runs 2/0 gauge wires to the Giandel inverter, which runs 3 - 6 gauge wires to the 30 amp breaker, and 30 amp plug socket.

- - - - - - - - - - - - - - - - - -

Physical Location Information:
Located approximately at: 40.963, -74.593
Approximate Sun Angle: 45 (degrees from horizon)

Load Test Information:
At first I was running a lighter load on the system for a solid hour, approximately 1000 watts (dometic fridge, computer electrical, motorhome aux batt charge controller).
The system was maintaining full batteries like this for the one hour, producing the following numbers.

New System:
18.8 Volts
8.4 Amps

Old System:
Did Not record
Did not record on start

Batt Indication:
Start: 14.2
End: 13

After seeing virtually no change, and lower solar input than expected I decided to increase consumption by adding another 1500 watts to the mix. I thought that by doing this the Charge Controller would open more and allow more throughput to go to the batteries.

New System:
16 Volts
16.1 Amps

Old System:
18 Volts
6.4 Amps


Final Thoughts and Concerns....
The wires run from the solar panels down the roof of our RV (by fridge) 10ft then under vehicle approximately 9ft to the mppt charge controllers.

I really have no idea why the input is looking so low, seems like each array is only producing 1/4 of the power they are rated to produce.

Before adding the new panel configuration the old configuration had been running 400+ watts pretty easily on a full sun day.

Really seriously appreciate any and all troubleshooting, input, or other help you all may be to provide...
 

Attachments

  • PXL_20221202_171223781.MP.jpg
    PXL_20221202_171223781.MP.jpg
    195.8 KB · Views: 6
  • PXL_20221202_184709360.MP.jpg
    PXL_20221202_184709360.MP.jpg
    519.5 KB · Views: 6
  • PXL_20221202_154434675.jpg
    PXL_20221202_154434675.jpg
    199.8 KB · Views: 6
  • PXL_20221202_184723803.jpg
    PXL_20221202_184723803.jpg
    392.4 KB · Views: 5
  • SolarConfig.png
    SolarConfig.png
    55 KB · Views: 5
If you think your PV output is low, I'd recommend disconnecting all of them and measuring voltage and current of each one charging individually.

I suspect the two shaded panels near the AC are doing nothing for you in the attached picture.

Then you have 3 panels at a poor sun angle that will significantly cut down their production. But I still would expect those three in total to output at least the spec sheet rating of one panel.

Make sure the battery voltage is low enough the charge controller is in bulk or constant current mode.
 