Using Schneider AGS with 7.5kW Onan JB Propane

ElectricIslander

Solar Enthusiast
Joined
Dec 29, 2020
Messages
227
Location
British Columbia, Canada
Hi (General edits to this post made to add info and correct genset type to 3 wire start)

Has anyone experience with wiring an old Onan 7.5kW JB remote start propane generator to the Schneider AGS?

Some old posts on the Smokestak generator forum said that this generator is a three wire stop and start setup: "Your genset is a 'three-wire' start and stop. Connect common to start to crank and start, disconnect after the start, the genset continues to run. To stop, connect common to stop while genset is running, genset will stop, then disconnect stop from common. The start and stop switch closures are momentary, only held for as long as needed."

It's not very clear from the Schneider AGS documentation which of the 14 types of wiring setup is applicable but there are types for both three wire and two wire start systems.

The Onan Model number is 7.5JB-3CR/12037AD, serial #C840719042. Below is a photo of it, it has a momentary start-run-stop toggle on the control box. Below is also a schematic showing the start-run-stop toggle switch S2 connections in upper center, with red circled terminal numbers 1-3.

I'd think that all that's needed at minimum would be to parallel the AGS Start / Stop lines to the toggle switch with two wires for Start (Terminal 3: start wire grounded), and Stop (Terminal 2: stop wire grounded) and add a run sense wire to verify to the AGS that genset is running? (Not sure how I'd create a run signal - the thread suggested to "use a relay and the centrifugal switch to send a signal to the Stop terminal when the external two wire circuit is opened, and until the set slows to the point that the centrifugal switch opens"). Apparently a run signal isn't really needed as the AGS generates that internally from the XWPro which signals when AC power is present on it's input.

The AGS setup would seem to be either Schneider AGS Type 8 (works with either 2 or 3 wire) or more likely Type 10 (Three Wire?) which has separate Start, Stop and Run wires. In either case, it's not really clear which wires are counted as the "2 or 3 wires" (perhaps not counting ground? as there are 4 to 6 wires involved)
2024-08-27 17_58_32-Conext-AGS-Owners-Guide_975-0307-01-01_ENG.pdf - Type8AGS.png


2024-08-27 15_42_47-Conext-AGS-Owners-Guide_TYPE10.png


MarkedUpSchematic.png




1.jpg
 

Attachments

  • 2024-08-27 15_33_04-967-0500 Onan JB JC Genset Engine & Magneciter Gen-end Service Manual (11-...png
    2024-08-27 15_33_04-967-0500 Onan JB JC Genset Engine & Magneciter Gen-end Service Manual (11-...png
    308.6 KB · Views: 7
Last edited:
I think you should start by hot wiring the generator to figure out what you need to start and stop the generator.

I can picture two different ways to interpret the info you found on a forum. Plus it's an old generator, things might have changed since they built it.
 
Good point, I think the wiring connection from the AGS to inside the generator is really simple (ie emulate the toggle switch to ground either start or stop momentarily) since the gen set has latching relays to just need momentary inputs for Starting (long enough for cranking) and Stopping (long enough for the internal run relay to dropout).

As for a run signal to the AGS from generator, I just noticed that according to the Schneider AGS manual, a run signal isn't actually required since the Schneider AGS monitors the GEN AC IN voltage to detect if the generator is running and modifies the start/run logic accordingly.
 
Last edited:
I will be watching this as I have an old Onan 2.5lk propane generator that has a similar if not the same start/stop control circuit.
Please post your results.
 
My money would be on the Type 10.
Schneider terminals 16, 18 -> Onan terminal 1
Schneider 17 -> Onan 3
Schneider 14 -> Onan 2
 
Onan of that era has pull down relays...
To start and stop you are grounding A2 on the relay coil to turn K2 on, and you are pulling K4's power source ( A1 )down to drop out the run relay.

Table two 2-14 is confusing I see the start relay but not the stop relay legend
I am not familiar with that controller.

Yes Type Ten would appear to be correct.....

And Saggys with the LK yes exactly the same. ( what is your model spec letter please Ill find you a print )

J range great units.
Don't screw it up parts are expensive
 
Last edited:
Onan of that era has pull down relays...
To start and stop you are grounding A2 on the relay coil to turn K2 on, and you are pulling K4's power source ( A1 )down to drop out the run relay.

Table two 2-14 is confusing I see the start relay but not the stop relay legend
I am not familiar with that controller.

Yes Type Ten would appear to be correct.....

And Saggys with the LK yes exactly the same. ( what is your model spec letter please Ill find you a print )

J range great units.
Don't screw it up parts are expensive
I have several models, will post nameplate tomorrow when I am on site, Thanks.
 
Here is the name plate of the one I am using.
 

Attachments

  • 20240904_145942.jpg
    20240904_145942.jpg
    191.9 KB · Views: 4
Yup the if a good unit
Edison three wire head

You have a spec E generator
If you have a failure of your generator charging cut out relay later spec lks used a large diode
That relay is obsolete and hard to find


I’ll get something for you soon
And now for something completely different

IMG_3118.jpeg
High compression cckb head from a tractor
Direct bolt on for your lk
Small improvement in fuel economy and better natural gas performance

IMG_0039.jpeg
The BGE Camel back head after some trimming on an lk
A much harder modification
For an incrementally small l improvement in fuel burn and power over the cckb head
But they us are much easier to find.

IMG_0017.jpeg
 
Last edited:
Excellent information! I have several of these, most LP fuel, one tri-fuel. I have been collecting them for over 10 years now.
One even has a load sensing relay that starts when a load is applied to the output. They are tough machines.
 
Is it safe to say I have the same start/stop control circuit as the OP?
 
  • Like
Reactions: DPC
My bad, I see the drawing is in the service manual you sent, Thank you!
 
  • Like
Reactions: DPC
Excellent information! I have several of these, most LP fuel, one tri-fuel. I have been collecting them for over 10 years now.
One even has a load sensing relay that starts when a load is applied to the output. They are tough machines.
Could I see that?
I have never seen that auto start feature and I would love to clone it...
 