Please take a look at my latest 12v system drawing to assure proper wire sizing, correct type fuses and their amp rating along with anything else you see that may not be acceptable. I have also included my energy audit summary for review.
Not in the drawing but I would like to add a Victron IP22 30a battery charger that I would like to add but wasn't sure how or the best way to do it. Can it simple be permanently attached to the battery posts or at the open fuse location in the Victron Lynx Distributor and plugged into shore power as wanted to charge batteries and use as shore power?
Thank you in advance for your help.
System size calculations | ||
Full Load W-hrs. | 1222.5 | W-Hrs. |
Full Load Watts | 1140 | Watts |
AC Watts | 1050 | Watts |
AC Surge wattage | 0 | Watts |
AC Watt-Hrs | 612.5 | W-Hrs. |
DC Watts | 90 | Watts |
DC Watt-Hrs | 610 | W-Hrs. |
Inverter Sizing | ||
Inverter efficiency | 85.00% | % |
Min continuous Inverter size | Watts | |
Min Surge Inverter size (Input Watts) | 1235 | Watts |
Battery Sizing | ||
Daily Storage Requirement | 1331 | W-Hrs/Day |
Max discharge from full CHARGE | 85.0% | % |
# days of storage capacity | 1.5 | Days |
System Voltage | 12.0 | Volts |
min Battery capacity W-Hrs | 2348.1 | W-Hrs. |
min Battery capacity A-Hrs | 195.7 | Amp Hours |
Max continuous current to DC Loads | 7.5 | |
Max continuous DC current to Inverter | 0.0 | |
Max continuous current from bat. | 7.5 | Amps |
Max Continuous discharge rate | 0.04 | C |
Solar Aray Sizing | ||
# sunny days to recharge while under load | Days | |
Required Total daily Solar output (Sunny) | W-Hrs. | |
Insolation # (Equivelent hours of full sun) | 0.0 | Hours |
Min Solar Cell Wattage | Watts | |
Max Charge Current | #VALUE! | Amps |
Max Charge rate | C |