Why do you have a 60A SCC for only 400 watts of panels?4 100w panels on series.
Open circuit voltage 90 or so....5 amps 70 ' run w/10ga wire....
Brand new AmpereTime 12v100ah and brand new victron 150/60 set to lifepo4 setting.
Thanks so much! I was rather alarmed lol. First day with this mppt!Most likely your batteries BMS disconnected due to one cell being higher than the rest. The high voltage recorded was probably just a spike as that happened.
Disconnect all connections to the controller for 3 minutes, (or turn off breakers if you have them). Re-connect and it should be fine.
After it is working, I would recommend setting your absorption voltage down to 14.0 or 14.1V. This usually helps with “runner” cells that charge faster than others and get out of range.
Agreed.Top balancing helps mitigate this, as well as having matched cells.
I think you have the option of auto selecting the battery voltage or setting the battery voltage via the app, try setting to 12v.
The issue could also be caused by an intermittent or faulty connection between the controller and battery.
If you have a breaker between the battery and controller, test, or bypass.
Its not impossible that the battery has a malfunction and is disconnecting. Note the maximum charge current for this battery is 50A.
Do you have an alternative battery , even a LA out of your car, to test the system performance?
A further point, did you let the Victron update to the latest softwere?
Mike
I would like to see a screenshot of your settings (main and screen you get to pressing the gear icon) and a pic of your battery/bms/inverter/SCC wiring.Any other input is greatly appreciated.
Will do!I would like to see a screenshot of your settings (main and screen you get to pressing the gear icon) and a pic of your battery/bms/inverter/SCC wiring.
Still working tonite at 75% .I'm leaning towards a faulty controller. I don't know where you got yours, but for me Amazon returns can get complicated after 30 days. The only test I can think of has already been mentioned, and that's try a different battery, even from a vehicle. I have an extra PWM controller and could test the panels and battery that way, but would not be worth the order and the wait.
Have you measured open circuit voltage on the panels? Mine is fairly close to the label. Nearly all 100 watt panels I look at are wired for around 18 volts and 6 amps, but occasionally I see one advertised at 36 volts and 3 amps. Short Circuit voltage on four panels in series like I mentioned could be more than the Victrion 150/60 could handle.
To me your charge settings look good. I thought perhaps the temp compensation was on and at a bad level, but it is disabled so it will stay at 14.2 or 13.5 regardless of temp.
What I find odd about your screen shot of the Victron app is the Solar Voltage is .35 volts and 0 amps. To me that says the panels are disconnected or its dark out. For me, my Victron App may read .1 volts and 0 amps when I flip the circuit breaker or its night time.
I'm sure you've seen this because like you say its a charger or PV overvoltage:
View attachment 43588
I never measured more than 94 volts even at 20° FI'm leaning towards a faulty controller. I don't know where you got yours, but for me Amazon returns can get complicated after 30 days. The only test I can think of has already been mentioned, and that's try a different battery, even from a vehicle. I have an extra PWM controller and could test the panels and battery that way, but would not be worth the order and the wait.
Have you measured open circuit voltage on the panels? Mine is fairly close to the label. Nearly all 100 watt panels I look at are wired for around 18 volts and 6 amps, but occasionally I see one advertised at 36 volts and 3 amps. Short Circuit voltage on four panels in series like I mentioned could be more than the Victrion 150/60 could handle.
To me your charge settings look good. I thought perhaps the temp compensation was on and at a bad level, but it is disabled so it will stay at 14.2 or 13.5 regardless of temp.
What I find odd about your screen shot of the Victron app is the Solar Voltage is .35 volts and 0 amps. To me that says the panels are disconnected or its dark out. For me, my Victron App may read .1 volts and 0 amps when I flip the circuit breaker or its night time.
I'm sure you've seen this because like you say its a charger or PV overvoltage:
View attachment 43588