YES, Inverters R Us has the new 24V MP-II 2x120v model in stock and is shipping them immediately.Is the VICTRON 24V Multiplus II 2x120v Available for Purchase? If so, where? Anyone have a link for purchase?
I could be wrong but I think they already make one it's UK only ?? hopefully they build one that's compatible with US power soon. I don't remember what they call it? But I'm pretty sure it's what you're talking about.Now that they have gone to 24V and 48V input, they should think about a 5000VA version.
I have the Multiplus II 12V 2x120 installed in my 5th wheel. Replaced the Multiplus 12V 3000/120 I had.Do we have any owners of a Multiplus II 2x120V on the Forum yet?
The Multiplus II 2x120 is restricted to 120VAC output. Victron does have a different version that supports 230VAC 50Hz output MultiPlus-II Inverter/Charger 230VCan the Multiplus II 2x120v be used to output 230v 60Hz?
The Multiplus II 2x120 is restricted to 120VAC output. Victron does have a different version that supports 230VAC 50Hz output MultiPlus-II Inverter/Charger 230V
In stock and on the shelf: https://www.currentconnected.com/product/mp3k2x120/?attribute_voltage=24V
The inverters can be changed from 50hz to 60hz in the settings
You seem to know a great deal about the Multiplus II 2x120, so I’m hoping you can answer my question:The inverters can be changed from 50hz to 60hz in the settings
If you are in North America, you don't want a 230v Victron inverter. These are 230v from L to N, not from L-L, they don't have a centertap. I highly recommend against using transformers to create the neutral as well.
Two 120v inverters can be series-connected for 120/240v split phase, as needed in North America. This is optimally done with NON 2x120v inverters, rather the single 120v units (SKU PMP242305100)
Yes in addition to what I know, the company I run (Current Connected) employs some of the highest trained Victron technicians in the country, so we have limitless knowledge at our disposal. Victron has a TON of features, but they take a lot of reading and understanding to fully utilize.You seem to know a great deal about the Multiplus II 2x120, so I’m hoping you can answer my question
Yes, you could do this but if your loads are fed through the inverters, the inverter has built in current measurement, so the external CT's are not needed at all. You only need the external CT's if you are powering loads from grid/generator directly, rather than feeding them from the output terminals of the inverter. This model has a 50A input capability, so if AC input was present, you could add another 25A to it (3kva) for a total output of 75A per leg total with grid/generator present. If you adjust the input current limit, you would be able to output [input] + 25A, so if your input circuit was 20a, you could output 45A.Using 2 120V units (two PMP242205100s) I assume you can connect 1 to L1 with its external CT sensor connected around the L1 mains wire, and the second to
L2 with it’s external CT sensor connected around the L2 mains wire and in this way, you can offset both L1 and L2 loads on the AC Input as long as those loads are less than 2.4kVa per leg (4.8kVa total) and battery charge remains, correct?
Yes, Multiplus-2 2x120 is able to do a series / split phase 120/240v installation, but it has no advantage over a single 120v model. In this split phase configuration, you wouldn't want to take advantage of the L2 terminals at all, L1 feeds into inverter 1 (and is monitored by that CT), L2 feeds into inverter 2. This gives you powerassist on both legs, and operates as mentioned in previous paragraph.So my first question is to confirm that you can connect two Multiplus II 2x120s in the same way (one in L1, the other on L2, each with external CT sensors connected to their respective leg from mains) and they will function in the same way (assuming the non-inverted leg of AC output remains disconnected on both inverters).
Exactly...but it would be 3kva (2.4 kW)a Multiplus II 120x2 can be used to offset up to a maximum of 2.4kVA of all loads on L1 (both on AC input and AC output) by using the external CT sensor.
Cool. Assuming you sell at the same MSRP as your competitors, your company sounds like the kind of outfit I’d like to purchase a Victron from…Yes in addition to what I know, the company I run (Current Connected) employs some of the highest trained Victron technicians in the country, so we have limitless knowledge at our disposal. Victron has a TON of features, but they take a lot of reading and understanding to fully utilize.
I understand that. My goal is to offset loads on the AC input. I may eventually set up a small Critical Loads Panel for truly critical 120VAC loads such as refrigerators, but for the purpose of this discussion, assume I’ve left the AC output of both (or only one) Multiplus II 2x120 disconnected (floating) and I expect no functionality when the grid goes down…Yes, you could do this but if your loads are fed through the inverters, the inverter has built in current measurement, so the external CT's are not needed at all.
Precisely. This is exactly the capability I am interested in (using the external CT sensor clamped to the L1 mains wire.You only need the external CT's if you are powering loads from grid/generator directly, rather than feeding them from the output terminals of the inverter.
On the AC output, not that important to me. But offsetting loads connected to L1 input, power available would be limited to 2.4kVA / 3kW, correct?This model has a 50A input capability, so if AC input was present, you could add another 25A to it (3kva) for a total output of 75A per leg total with grid/generator present.
All of this is still for AC output, correct?If you adjust the input current limit, you would be able to output [input] + 25A, so if your input circuit was 20a, you could output 45A.
I’m open to either dual Multiplus II 120Vs or dual Mutiplus II 2x120Vs. Since the 24VDC 2x120V models have launched, it seems as though the 24VDV 120VAC Multiplus IIs have pretty much gone out of production (impossible to find).Yes, Multiplus-2 2x120 is able to do a series / split phase 120/240v installation, but it has no advantage over a single 120v model.
This is the capability I’m looking for. I spoke to one of your competitors (another US Victron reseller and after checking with his ‘expert’ (who apparently has a Myltuplus II 2x120 at home), he told me that the CT sensor was only usable for monitoring in the US 120V models and could not be used to offset load on the AC input even though that functionality was supported in Europe.In this split phase configuration, you wouldn't want to take advantage of the L2 terminals at all, L1 feeds into inverter 1 (and is monitored by that CT), L2 feeds into inverter 2. This gives you powerassist on both legs, and operates as mentioned in previous paragraph.
I must confess this distinction continues to befuddle me. I used to make the same distinction you and Victron do but so many vendors now use 3kW and 3kVA interchangeably that I guess I’ve started to go with the flow.Exactly...but it would be 3kva (2.4 kW)
Yes, we sell at MAP, the lowest we are allowed to advertise at. Everyone sells at MAP, no one buys at prices over MAP...MSRP as your competitors
My goal is to offset loads on the AC input
OK no problem. We will focus on that for now.CT sensor clamped to the L1 mains wire
Not at all. The local Victron warehouse has 280 in stock...I just ordered some in and will have them on my shelf in 2 days - I don't stock many because just about everything in 24v sells at a snail's pace...everyone either uses 12v or jumps to 48v.the 24VDV 120VAC Multiplus IIs have pretty much gone out of production
Sort of. The inverter cannot interact with an l2 coming in, only feed it through. The CT would only be able to interact with L1.CT sensor was only usable for monitoring in the US 120V models and could not be used to offset load on the AC input
Sounds good.kW is what matters so let’s just stick to 2.4kW
Cool.Yes, we sell at MAP, the lowest we are allowed to advertise at. Everyone sells at MAP, no one buys at prices over MAP...
Great.OK no problem. We will focus on that for now.
OK - I’m open to the 24V Multiplus II 120V, especially if it is cheaper. If the only difference between a 120x2 setup and a 120x1 setup in the 120x2 allows 240VAC loads on the Critical Loads Panel tone powered while the grid is up, that is not a use case so will ever be interested in (any Critical Loads Panel I establish would be 120VAC loads only).Not at all. The local Victron warehouse has 280 in stock...I just ordered some in and will have them on my shelf in 2 days - I don't stock many because just about everything in 24v sells at a snail's pace...everyone either uses 12v or jumps to 48v.
This is what I expected and what I explained to the other rep, but he seemed quite certain no load compensation on L1 only was possible.Sort of. The inverter cannot interact with an l2 coming in, only feed it through. The CT would only be able to interact with L1.
And that about another $500 if so? Needed with either 120x2 or 120?You must have a Cerbo-GX.
What I was hoping. Setpoint can also be set a bit higher (or lower if negative) maintain a small amount of import such as 20W if you want more margin to avoid export, correct?First, you would need to load the ESS assistant into the inverter with Victron Connect / VEConfig.
Second, on the Cerbo-GX, you would go into the ESS menu, and set the grid setpoint to 0w.
Nice. What is the longest cable length supported?When you plug the CT into the inverter, it automatically detects and enables it.
You’ll be my hero if you can do this. I’m primarily interested in using the MPII to offset overnight load associated with refrigerators powered by the main panel, though high intermittent loads of 3kW @ 240VAC (translating to 1500kW on L1) associated with the heating element of the electric oven duty-cycling is the highest load I’d ever be (fully or partially) offsetting on L1.I will gladly do a setup on my bench tomorrow to be 1000% certain and share the results.
I’ve seen that picture before but am confused enough now that perhaps you can help me to understand something: