Jeffz
New Member
Hi Will i'm a new member to the form could you [please post a video of how to install a Victron class t fuse holder.
Regards,
Regards,
You're referring to the Lynx Class-T Power In? https://www.victronenergy.com/dc-distribution-systems/lynx-class-t-power-inHi Will i'm a new member to the form could you [please post a video of how to install a Victron class t fuse holder.
Regards,
casually throws that out as I look at my 200Ah 12V system :-(small solar power system.
Wait, 18 of those server rack packs? Really? That's enormous. So you're going to be doing 18 in parallel? Um. I think the general recommendation is each pack in parallel should have it's own Class-T fuse, so that if one pack/cell goes bad with a dead short, it will blow it's fuse and take itself out of the system, and the rest of the packs will be OK.Hello thank's to everyone that repled my battery bank is 92.16 kwh it consists of three server racks of 30.72 kwh each for a total of 18 EG4 lifepower 4 V2 batteries so i need 3 class T fuses one on each server rack that's why i purchased 2 Victron class T fuse holders that will hold 4 class T fuses 2 in each module and 2 Victron power-in modules. I also have 2 EG4 12000xp inverters well that's the run down of my small solar power system.
These have integrated dc breakers and don't need a class T imo.i think i've decided to go with two of the eco-worthy 100 amp 51.2v server rack batteries . do they make class T fuses small enough for each of them ? or should i run the pair into a single 225-250 amp class t fuse ? or is 225-250 adaquate protection for each one ? if a smaller class-T for each is recommend can some link to the fuse ?
thanks , jeff
Oh boy - doesn't this go against what most people post here?These have integrated dc breakers and don't need a class T imo.
I think you mean the dc breaker seizing up. Not the t-class fuse.Or it's even high enough to spot weld it closed and keep it from tripping.
So a Nader 125A breaker has an AIC of 10,000A. Not as good as a class T at 20k or an mnedc250 at 50k but well beyond a megafuse with maybe 2k rating. I use mnedc250s on my batteries that don't have integrated breakers, for the two rack mounts I do rely on the integrated breakers.Oh boy - doesn't this go against what most people post here?
I think you're saying that the battery, because it has a DC breaker, doesn't itself need a T-class (it doesn't have one inside it), but if connecting this server rack battery to a bus bar, it absolutely should have a T-class fuse? 100 is a lot of amps...that'd be one heck of a fire.
In this situation, you are still using t-class fuse though, yes?I use mnedc250s on my batteries that don't have integrated breakers
Yes, that's what I meant, the DC breaker getting spot welded closed, so continuing to pass current.I think you mean the dc breaker seizing up. Not the t-class fuse.