I'm doing a new RV install and I know just enough to be dangerous.
(Qty 10) JA Solar JAM72D30-545/MB Panels - Bifacial 545w
Voc 49.75V
Vmp 41.8v
Isc 13.93A
Imp 13.04A
48v System feeding 2 48/3000's in parallel
I ran it through the Victron wizard and its recommending:
PV min. voltage at 140°F70V
PV max. voltage at 14°F109V
MPPT max. output current85A
PV min. current at 140°F85A
** Power limiting @ high temp.
PV max. current at 14°F85A
* Power limiting @ low temp.
PV Power Ratio: 111%
This would be with the panets wired as 5 strings of 2
Thoughts? I love the idea of only needing 1 controller, but is this really the best way to skin this cat?
Thanks
Liam
(Qty 10) JA Solar JAM72D30-545/MB Panels - Bifacial 545w
Voc 49.75V
Vmp 41.8v
Isc 13.93A
Imp 13.04A
48v System feeding 2 48/3000's in parallel
I ran it through the Victron wizard and its recommending:
SmartSolar MPPT 150/85 Tr VE.Can
MPPT max. input voltage150VPV min. voltage at 140°F70V
PV max. voltage at 14°F109V
MPPT max. output current85A
PV min. current at 140°F85A
** Power limiting @ high temp.
PV max. current at 14°F85A
* Power limiting @ low temp.
PV Power Ratio: 111%
This would be with the panets wired as 5 strings of 2
Thoughts? I love the idea of only needing 1 controller, but is this really the best way to skin this cat?
Thanks
Liam