There are two versions of the 120V Victron Phoenix Inverter VE.Direct for the US – NEMA 5-15R and GFCI. I have found online inconsistencies regarding the internal neutral bonding capabilities.
The manual apparently covers both models. Appendix A in the manual states there is an internal jumper. Online references state the NEMA 5-15R model has the jumper and the GFCI does not (although I did find inconsistencies is that assessment.)
I also found references to model and manual updates, but can’t confirm release dates.
Can Victron Phoenix Inverter with VE.Direct users/owners verify the presence/absence of the neutral bonding jumper?
Manual: https://www.victronenergy.com/inverters/phoenix-inverter-vedirect-250va-800va#manual
Update 5/20/22
I purchased two Phoenix VE.Direct Inverters: 12V 1200VA 5-15R and 12V 500VA GFCI. Both have the capability to change the neutral bonding (bonded to non-bonded) via an internal jumper wire as described in the manual. I verified the capability by testing continuity with a multimeter.
Also, the GFCI is tamper resistant.
Update 5/20/22