Okay friends, testing completed earlier today.
Questions I'd like answers to:
1.) Why the difference in SOC between the battery BMS and the Victron shunt.
2.) Why the difference between current readings between the BMS and the Victron shunt
3.) Recommendations on configuration of the JBD BMS to make it more accurate. Happy to use JBD app or Overkill Solar app.
4.) How to change things up so that the low SOC and low voltage coincide with the inverter shutting off. When discharging at 100 A, I have 4 audible alerts, and about 14 minutes max from the time I get a Low SOC alert and inverter dies. inverter not configurable (Giandel 12V).
Here's my findings:
Current differences:
There was always a current difference between the BMS and the Victron. While the current would fluctuate, the load is a pool pump running at 3120 RPMs through inverter through fuse through bus bar through kill switch through T-class to battery. Negative side is just from inverter through inverter shunt (for testing) through bus bar through battery shunt (measurements I used) through to the battery.
State of charge differences:
Seems the differences get more and more the lower the SOC is. Notice that even before starting, the victron thought SOC was lower by 7.8%, and before inverter shutoff it was 27.2% difference. That's not great. Over the course of the hour and a half test, the average difference was 15.5%. Here's the measurements:
Maybe there's some sync button in the BMS for low SOC? I know there is one for the 100% SOC in the victron and I presume in the BMS as well. Was pretty sure I had done that already when at full SOC over the weekend.
Temperature Differences:
Temp measured with infrared by pointing at battery conductor lug at T-Class fuse. Pointed at wire, at lug, and shrink wrapping; number posted is max number I got. I know it is a reflective surface, but still, not getting 70+ degrees C like I was with old BMS and conductors.
The BMS's internal temp sensor (wire taped to top of cells with Kapton tape) seems to be closest in number to the victron temp sensor I have on the top of the cells about 1/4" away from the taped one. The biggest difference is between the Ruuvi and the other two temp sensors about a 2.55 degrees C difference. I'm okay with that, but seems that the Ruuvi always will report 'colder' than something taped directly to the cells.
Here's the temp measurements:
The highest reading I got was 93 degrees F or 34 degrees C, and when I touched the wires - positive - they were warm but not hot. It almost seemed like the rubber casing around the conductors were 'loose' - like a wire labeled as 6 AWG was actually 8 AWG inside (using a guess / making an analogy / not facts / trying to explain). Just seemed like air was between the hotter wires inside compared to shething outside for those conductors coming off battery. But again, 93 degrees F for wire rated probably for 200 degrees F, not sure I need to worry? Remember my old conductors were getting 160 degrees F before, and in 1/5 the time (much faster - in 15-20 minutes, very hot).
Notes/Log:
Everything was doing great until around the 90 minute mark. It was acting as it should, just inaccurate readings.
At 10:45 AM, VRM reported a low state of charge, likely when reached 10% or 5% - whatever it is setup to alert me at. I expected this.
At 10:50 AM, while watching battery BMS, it jumped from SOC of 27 down to zero in seconds. At this time, the battery voltage went from 12.06 V to 12.00 V in the BMS very quickly. It was almost like the BMS is configured to be 12V=0% SOC. I'm aware of the steep curve with LiFePo4. Well at least aware of it, not an expert. Guessing config issue with BMS?
At 10:55 AM, Victron low voltage alarm, which I expected.
At 10:59 AM, non-Victron inverter died due to low voltage protection. You cannot change this voltage. I think it is set to 11.5 V; Battery BMS said 11.5V. I get four audible beeps from inverter, then it shuts down - that's very fast when discharging at 100 A.
It never hit low voltage protection in battery on this test - would not want it to, but was probably about to. It did the other day when I tested, but I think I had current up even higher (maybe to 150 A for that test).
At 11:03 AM, turned inverter back on, along with breakers, disconnects, etc and started the SCC back up and running to charge battery back up.
Victron VRM reports consumption at 2.5 kWh for this test, since midnight with the idle consumption.
Victron Connect app reports consumed Ah at 197.8 Ah (200 Ah battery) after the inverter shut off. There is still likely that 2.2 Ah left. I have done 200 Ah discharge tests before successfully.
After starting the SCC back up, it took over an hour for the shunt to report anything above zero percent state of charge. That seems strange to me, as it was charging around 15 Amps for almost an hour. About 7 A when started back up (cloudy day) and about 30 A when I just checked, so calling it 15 A on average during the hour.
Thank you all so much for reading and following along.