I can’t figure out what I’m missing here, all my voltage settings are below my thresholds and it will not charge, it shows 150volts input. Any help is appreciated!
What are your voltage settings and what are your thresholds?all my voltage settings are below my thresholds
How are they wired? If all in series, your SCC is likely shutting down from over voltage (4x 40V = bad)The panels are 4x 320 40voc
That charge controller is rated for 250V so that is not an issue so all can be wired in series with no issue.How are they wired? If all in series, your SCC is likely shutting down from over voltage (4x 40V = bad)
I tried to use one single panels as well with same result.How are they wired? If all in series, your SCC is likely shutting down from over voltage (4x 40V = bad)
Did you connect battery first?
Happen to have a screenshot of your Victron app?
Are your batteries fully charged?
Yes I get this. My bms is on, I can apply charge current with a different charger and the remote jumper they are talking about there is there.Have you clicked on the "Why is the charger off?" link? Or tried turning it on?
Battery and panels is all.What connections have been made to your SCC? Most importantly, is there a cable connected to the VE.Direct port? If so, to what? Anything in the remote or relay connections?
YesDid you disconnect the battery (after disconnecting the PV) and then reconnecting the battery (before reconnecting the PV)?
Not to my knowledge, it’s the overkill style bms. Would it be safe to bypass the bms for testing purposes?Is there someway to reset the BMS?
Yes and yesDo you have another charging source besides the SCC? Does that other charging source work at the moment?
No it came like that and from what I can tell in the manual it’s the bypass unless you have the remote bms from Victron.I think the BMS message is a red herring. The jumpers on the SCC seem to make it think there is a remote switch or BMS telling it to turn off. If you have sufficient battery voltage, i'd say it is mighty unlikely its your BMS (i have a couple Overkills so know about that a bit).
Did you specifically put the jumper on your SCC? I cannot remember doing anything with any jumpers... not sure if it was on or in a bag in the box. I will go out and see what i have on my 100/30.