Hey there, I have a victron system with a Quattro and I want to use the eg4 Chargeverter.
Am I okay to connect the chargeveter cables to the busbars?
I have a 48 volt battleborn battery bank.
See photos.

Thanks for the help.
 

Attachments

  • IMG_1246.jpeg
    IMG_1246.jpeg
    320.5 KB · Views: 10
  • IMG_1084.jpeg
    IMG_1084.jpeg
    442.2 KB · Views: 10
Yes. Fuse/breaker the (+) conductor.

 
The chargeverter cannot put out more than 100A.
I fused my + chargeverter connection to the + busbar at 125A.
The chargeverter has its own DC breaker, but I certainly do not trust it.
 
Thanks. Any idea on how to calculate the fuse size ? The generator can put out 7500 watts
The Chargeverter is rated to push up to 100 amps. That works out to just a bit over 5,000 watts, so your generator should be able to top it out. The 125 amp suggestion is good to prevent false trips. Make sure to run cable that is safe at 125 amps.
 