There's a guy on Youtube claiming to be able to power his whole home, charge one or more Tesla(s) and do it with two 6k inverters, four batteries and 12k of solar PV.

Most of yall already know most of this. Some don’t. Not criticizing the approach here – just sharing a different approach based on the various experiences we encountered as we started with our first 4.1 Kw solar system and have now progressed to the 16.8 Kw system we have today.Note: Its actually against the law in every state to attach a power system to your home, if your home is connected to the grid, and said system is not completely inspected by a licensed and bonded agent of the utility service. Also, you might not be covered by your homeowner insurance in the event something goes haywire if it wasn’t approved and inspected by your utility service. Its called “an interconnect agreement”. Simply having an interlock installed in your primary load center may be insufficient and a violation of your utility service providers power agreement, city, county, state or National Electric Code requirements. That breaker in your panel doesn’t provide much of an “air gap” to disconnect your system from the grid. Conversely, a true manual and/or automatic transfer switches will “air gap” the disconnect sufficiently to prevent almost all possibility of a power bridge. So know what the code is for your locality before connecting an inverter or standby generator into your electrical system.

A homeowner can save a bunch of money if everything they install is MANUAL. The problem with little or nothing being automatic is little or nothing is protected from errant voltage (lightning / EMP) that originates from the grid. MANUAL also requires the homeowner to be HOME when the power fails, otherwise all of their frozen and refrigerated goods will be thawing out starting the moment the lights go out.

A fully AUTOMATIC system is (arguably) twice as expensive as a manual system. Sure there are exceptions. And yes, fully automatic means just that – completely hands off.

AUTOMATIC means the system continues to power the appliances when the grid fails. If sufficient quality components are installed and the system is hardened against lightning/EMP there is a very good chance nothing will fail and all of your freezers and refrigerators will continue in operation uninterrupted. You’ll come home to the lights on, hot water being available and your home environment being comfortable, even if the grid power is down.

A MANUAL system that experiences an outage with the homeowner away from home will result in a decline in the set point temperatures for all of the various appliances – resulting in a “call” for those appliances to turn “on” as soon as power is restored. This creates a whole new problem in itself. When the homeowner returns home and notices that the lights are out, and turns on the MANUAL system, ALL of the appliances that have thermostats (water heater, HVAC, refrigerator, freezer, spa, pool, etc) will instantly be in “call” (need to be “on”) and with so many appliances in demand at the same time, the battery based inverter system will trip into overload. The homeowner will then have to play the shell game to incrementally isolate the things they want on first and last to recover their living environment.

An AUTOMATIC system (typically costs a lot more) includes an Automatic Transfer Switch (ATS) that disconnects the system from the line side of the grid when grid power fails. This is an interconnect requirement to prevent homeowners from accidently designing systems that can kill a lineman up the street trying to restore grid power.

Well designed automatic systems will delay the start of a standby generator if sufficient power is available via battery or PV to meet the load demand. As the batteries deplete, and with no PV present, smart inverters can be programmed to use the two wire start feature to automatically start a standby generator, which will then be used to recharge the batteries and meet the load demand of the appliances installed in the home. Typically, as the charge reaches about 95% the smart inverter will send a “stop” command to the generator, disconnecting the generator and resuming battery only usage until grid power is restored, the sun comes up or it enters into another standby generator run cycle.

MANUAL systems are easily overloaded. Its easy to demonstrate that a system might be able to run a household for 15-30 minutes without a problem. The real measurement is to turn the grid power off, touch nothing else, and see how long it will operate before the combination of subsequent events causes an overload. Bring a flashlight – its going to happen.

On a manual system its inevitable to overload. It will especially overload if the homeowner is not home. All it takes is for the water heater and the spa to be on at the same time and the HVAC system have a “call” and POP! And that’ll be the end of the power going to your refrigerators and freezers until you get home and go through the manual switchology to isolate those large appliances. Oh, sure, some inveters will reset themselves and turn back on, only to again encounter an over demand and trip off again. Some inverter manufacturers software will recycle this three times and then stay off.

Oh, and don’t think it’ll be a simple switch this and that and everything will be normal in 20 minutes. Not so fast. Those refrigerators and freezers might have 2-10+ degrees to recover, and that’ll mean the duty cycle will be 100% for an hour or more as they cool things back down. Then your water heater will have the same demand, as will the spa and HVAC systems. It could take HOURS to bring things back to normal, assuming you have enough battery power stored to accomplish the task. In a manual system, It can take longer to restore normalcy than the amount of time the power was actually off.

So while you are running around trying to hobble together a power management plan and an order of merit for what needs power first, someone in the house throws something into the microwave and this high power consumer trips the inverter as you are sitting there trying to squeeze out the best efficiency options you might have thought you had. Or, your wife starts a hair dryer after taking a bath, and the combination of the water heater (5500 watts) trying to restore the heat in itself after her bath, combined with the 1600 watts draw of the hair dryer, and the 1100 watts drawn from the coffee maker, and suddenly everything gets quiet. Poof! Lights out!

What most people need to know is: Without batteries attached to a charger/inverter, solar panels will turn off when the power goes out. That means they will NOT supply power to anything unless they can (at a minimum) detect a stable sine wave that (here in the US) meets the UL-1741 standard. Most standby generators will not meet this standard, and any attempt to use a small generator in tandem with solar panels will result in damage or a dysfunctional system.

Small generators (typically <20Kw) can’t maintain 60 hertz plus or minus 0.5 hertz, nor can they maintain the voltage at 120/240 VAC plus or minus 7. Our 20Kw B&G generator won’t produce stable enough power to satisfy the tight parameters designed in to all microinverters, so a large (< 5K) inverter is required to manage the standby power source. You simply cannot use microinverters with a standby generator alone. This might surprise some, and folks on here might claim that they’ve got it to work, but it (UL1741) is intentionally designed to preclude these things working together reliably. I know, because we had to replace our microinverters on the first setup twice and go to a standard MPPT controller/inverter and eventually wire that Solaredge system away from the standby generator power source.

We now have three primary load centers. #1 is controlled and powered by the twin 12k Sol-Arks, getting its power from grid, solar, battery and standby generator. #2 is powered by grid and standby generator only. #3 is powered by grid only, but has the Solaredge feeding into it to reduce the grid load demand during the day.
 
Batteries are a must because household loads will start and stop, causing large variations in the frequency and voltage loads, which will fall outside the UL-1741 standards, which will cause different components to disconnect from the system leading to a cascade and a complete power outage. Adding batteries to the inverter will help, but not solve the incompatibility variable. So pick your standby generator wisely, and don’t assume that a Generac standby generator will work with a Generac Powerwall – it won’t. More on that some other day.

Sizing your battery storage is a simple function of how much power in watts are you going to draw at any given moment. Using arguable numbers, if your water heater, HVAC, lights and two refrigerator/freezer compressors were to all have a call for power, its not inconceivable to see a sustained start surge in excess of 60 amps @ 240 VAC (14,400 watts). Yes, some inverters are capable of handling a momentary surge, but it won’t be momentary if you have a 5500 watt water heater latched “on” while the other appliances enter into a start envelope. The number of batteries necessary becomes a function of surge wattage and wire sizing. If the batteries are paralleled with sufficiently sized cabling, and the primary leads are as short as possible, the minimum number of EG4’s is four. Four of them will not be capable of providing power to a whole “normal” home for more than a few hours. Look at your power bill. Do the math and calculate how many kilowatts you use per day, on average. If you and everyone in your home is away from home during the day, most of your consumption happens when you are home. If you are home during the day and the sun is shining, and your solar system is charging batteries, you have the maximum amount of power that your inverter will ever be able to achieve. Why? Because it has power available from the sun, batteries and the grid. Take away one or two of those options and your inverter will no longer be able to do as much. Most inverters have “pass-through” power, which means if they are grid tied they will suck excess power from the grid or from a standby generator (assuming its operating) to “boost” the power as different appliances start. If the grid is not available and the standby generator is not in operation, start loads will peak the inverters capacity quite easily. If you are sufficiently sized and have enough battery power everything will function fine. However, as your batteries deplete, and depending on their chemistry, the inverter will soon be unable to handle large start surges because the battery voltage will fall below minimums during the surge and the inverter will trip. A good rule of thumb is to calculate your daily consumption of kilowatts and have at least 50% of that covered in battery storage. Anything less and you are looking at repeated run cycles on the standby generator – which might not be ideal if you are trying for discretion.
 
There's a guy on Youtube claiming to be able to power his whole home, charge one or more Tesla(s) and do it with two 6k inverters, four batteries and 12k of solar PV.
...
Heck that's nothing. I run my house, power the neighborhood, mine thousands of Bitcoins, run an illegal grow operation, and still have enough left over PV production to waste on watching boring Youtube videos. I do it all on a few 100w RV panels, 1 battery and a small 12vDC- 10,000w inverter.
 
There's a guy on Youtube claiming to be able to power his whole home, charge one or more Tesla(s) and do it with two 6k inverters, four batteries and 12k of solar PV.
I did not read your post because it was too long. I have 10 kW of solar, one SolArk 12k , and 20kWh of batteries and I can run my house.
 
OK. interesting post. maybe presented in a slightly know it all manner....

I agree that trying to get a fully automatic/smart load shedding/complete backup/while away from home/never fails
system may require a crack pipe and/or a millionaires budget

to get maybe 90-95% is easily doable, and many of us have
I have both grid tie and off grid systems. I can control HVAC thru internet if away
water heater is on a dedicated grid circuit, will not run if grid is down
everything else is off grid with 30kwh batteries.

if grid is down and batteries down, need to manually start gen with chargeverter, even this could be automated
 
I believed you until this!
That is the one real thing in my entire post. (not that I have one or would ever want one)

"This 10000 watt 12 volt inverter is the best on the market in its class . This inverter can handle nearly any application with its 10000 watt continuous capacity and 20000 watt surge capabilities (40 milliseconds). The Inverter Store sells hundreds of large 12 volt inverters every month, which is why we carry AIMS Powers newest most innovative version of the product in stock. This inverter is the first of its kind in terms of size and weight, making it far more flexible than any other inverter this size. Whether planning to use this inverter for off-grid cabin applications, mobile business or for a back-up power system in your home, this inverter will get the job done while also taking up the least amount of space possible. The biggest innovation regarding this inverter is its weight: a mere 21 pounds, which is unrivaled by any other inverter on the market with that wattage capacity. Its size is also remarkable, because it takes up less than half the space older models require. For jobs that require a lot of power, youd usually have to lug out an inverter thats more than 40 pounds, but those days are over thanks to AIMS Powers game-changing technology featured in this special 10000 watt 12 volt modified sine inverter. Converting DC to AC for you entire home no longer requires an inverter that weighs as much as a boat anchor, and you can thank this product! [FEATURES] 10000W max continuous power Modified sine wave with Pulse Width Modulation technology (soft start) Volt meter on front panel to monitor your battery voltage Amp meter on front panel to monitor your current use (rate at which battery is drained) Over Temperature LED indicator Over Load LED indicator AC direct connect terminal block On/off switch Over Temperature protection Over Load protection Single cooling fan thermally controlled Internally fuse protected AC output short circuit protection Auto reset on most fault conditions Aluminum case for optimal cooling Pre-wired for remote on/off switch Pre-slotted mounting plate [SPECIFICATIONS] Continuous output power: 10000 Watt Surge power capability (peak power): 20000 Watt DC input / operating voltage: 10 to 16 volts Output voltage: 120 volts AC +/- 10% Output wave form: modified sine wave with phase correction Output frequency: 60 Hz +/- 1 Hz Battery low voltage alarm: 10. 5 +/- 0. 5 volts Battery low voltage shutdown: 10. 0 +/- 0. 5 volts No load current:"

1711206054277.png
 
That is the one real thing in my entire post. (not that I have one or would ever want one)

"This 10000 watt 12 volt inverter is the best on the market in its class . This inverter can handle nearly any application with its 10000 watt continuous capacity and 20000 watt surge capabilities (40 milliseconds). The Inverter Store sells hundreds of large 12 volt inverters every month, which is why we carry AIMS Powers newest most innovative version of the product in stock. This inverter is the first of its kind in terms of size and weight, making it far more flexible than any other inverter this size. Whether planning to use this inverter for off-grid cabin applications, mobile business or for a back-up power system in your home, this inverter will get the job done while also taking up the least amount of space possible. The biggest innovation regarding this inverter is its weight: a mere 21 pounds, which is unrivaled by any other inverter on the market with that wattage capacity. Its size is also remarkable, because it takes up less than half the space older models require. For jobs that require a lot of power, youd usually have to lug out an inverter thats more than 40 pounds, but those days are over thanks to AIMS Powers game-changing technology featured in this special 10000 watt 12 volt modified sine inverter. Converting DC to AC for you entire home no longer requires an inverter that weighs as much as a boat anchor, and you can thank this product! [FEATURES] 10000W max continuous power Modified sine wave with Pulse Width Modulation technology (soft start) Volt meter on front panel to monitor your battery voltage Amp meter on front panel to monitor your current use (rate at which battery is drained) Over Temperature LED indicator Over Load LED indicator AC direct connect terminal block On/off switch Over Temperature protection Over Load protection Single cooling fan thermally controlled Internally fuse protected AC output short circuit protection Auto reset on most fault conditions Aluminum case for optimal cooling Pre-wired for remote on/off switch Pre-slotted mounting plate [SPECIFICATIONS] Continuous output power: 10000 Watt Surge power capability (peak power): 20000 Watt DC input / operating voltage: 10 to 16 volts Output voltage: 120 volts AC +/- 10% Output wave form: modified sine wave with phase correction Output frequency: 60 Hz +/- 1 Hz Battery low voltage alarm: 10. 5 +/- 0. 5 volts Battery low voltage shutdown: 10. 0 +/- 0. 5 volts No load current:"

View attachment 203956
Who wants to get this just to test their claims?
 
On a manual system it's inevitable to overload. It will especially overload if the homeowner is not home. All it takes is for the water heater and the spa to be on at the same time and the HVAC system have a “call” and POP!
That's the trick though, I don't have an electric spa or water heater.
 
Simply having an interlock installed in your primary load center may be insufficient and a violation of your utility service providers power agreement, city, county, state or National Electric Code requirements. That breaker in your panel doesn’t provide much of an “air gap” to disconnect your system from the grid. Conversely, a true manual and/or automatic transfer switches will “air gap” the disconnect sufficiently to prevent almost all possibility of a power bridge.

This is something I noticed and have thought about.

Circuit breakers do qualify as an "isolator". I think that is about 1" airgap (crammed inside a small molded case circuit breaker).
Visible blade safety switch is a large box, but if you examine it the blade doesn't pull all that far away from other contact. About 1".

Difference seems to be "visible blade", you can actually see it is open. That is what the utility required years ago.

A "supplemental protector" looks like a breaker but doesn't qualify as an isolator.


An interlocked breaker is sometimes used for backfeed by generator. Works the same backfeeding by inverter.
For an inverter, we put visible blade disconnect on its "grid" connection, where it implements UL-1741 anti-islanding and if firmware works right won't backfeed.
Output of inverter, fed to interlocked breaker, does not do anti-islanding.
 
That is the one real thing in my entire post. (not that I have one or would ever want one)

"This 10000 watt 12 volt inverter is the best on the market in its class . This inverter can handle nearly any application with its 10000 watt continuous capacity and 20000 watt surge capabilities (40 milliseconds). The Inverter Store sells hundreds of large 12 volt inverters every month, which is why we carry AIMS Powers newest most innovative version of the product in stock. This inverter is the first of its kind in terms of size and weight, making it far more flexible than any other inverter this size. Whether planning to use this inverter for off-grid cabin applications, mobile business or for a back-up power system in your home, this inverter will get the job done while also taking up the least amount of space possible. The biggest innovation regarding this inverter is its weight: a mere 21 pounds, which is unrivaled by any other inverter on the market with that wattage capacity. Its size is also remarkable, because it takes up less than half the space older models require. For jobs that require a lot of power, youd usually have to lug out an inverter thats more than 40 pounds, but those days are over thanks to AIMS Powers game-changing technology featured in this special 10000 watt 12 volt modified sine inverter. Converting DC to AC for you entire home no longer requires an inverter that weighs as much as a boat anchor, and you can thank this product! [FEATURES] 10000W max continuous power Modified sine wave with Pulse Width Modulation technology (soft start) Volt meter on front panel to monitor your battery voltage Amp meter on front panel to monitor your current use (rate at which battery is drained) Over Temperature LED indicator Over Load LED indicator AC direct connect terminal block On/off switch Over Temperature protection Over Load protection Single cooling fan thermally controlled Internally fuse protected AC output short circuit protection Auto reset on most fault conditions Aluminum case for optimal cooling Pre-wired for remote on/off switch Pre-slotted mounting plate [SPECIFICATIONS] Continuous output power: 10000 Watt Surge power capability (peak power): 20000 Watt DC input / operating voltage: 10 to 16 volts Output voltage: 120 volts AC +/- 10% Output wave form: modified sine wave with phase correction Output frequency: 60 Hz +/- 1 Hz Battery low voltage alarm: 10. 5 +/- 0. 5 volts Battery low voltage shutdown: 10. 0 +/- 0. 5 volts No load current:"

View attachment 203956
Wandering back thru. I call total BS. 10000/12 = 834A Your going to need a coupla 4/0 cables or maybe some 500kcmil, you ain't hooking all that to this thing. Gauge reads up to 120A, maybe 1500W (120X13). Which we plainly see on the label ("MAX 1500W). Not even 5000W. I think you'd struggle to get #4 connected to those lugs.
 
Wandering back thru. I call total BS. 10000/12 = 834A Your going to need a coupla 4/0 cables or maybe some 500kcmil, you ain't hooking all that to this thing. Gauge reads up to 120A, maybe 1500W (120X13). Which we plainly see on the label ("MAX 1500W). Not even 5000W. I think you'd struggle to get #4 connected to those lugs.
12v lugs seem to be on the other end of the inverter. Amp ”meter” seem to go up to 1200A and 1500W rating is for those wall outlets that are not rated for more than that anyways.
 