I'm hoping someone can confirm or correct my understanding of how to match your solar array strings to your charger/inverter. This is what I think is true:
Use VOC to make sure you do not exceed your inverter's capacity. Panel VOC x number of panels in your string x 1.2 (a rough constant to adjust for cold weather voltage boost) should be less than your inverter's max DC input voltage rating.
Use VMP to make sure you meet your inverter's MPP startup threshold. VMP at highest rated ambient temperature (since voltage drops as temperature increases) x number of panels in your string must be equal or greater to your inverter's lowest MPP operating voltage range.
Use LSC to ensure you do not exceed your inverter's maximum current capacity, that is, the maximum amps your controller can take. So LSC x number of parallel strings (if you are just running one string of panels in series the lSC is as rated for a single panel) must be lower than your inverter's maximum short circuit input current.
Is this roughly correct? Setting aside sizing an array according to your energy needs etc., etc., are these three factors what you need to use to make sure your inverter has enough juice to charge your batteries while not going boom?
Thanks in advance!
P.S. Is there a rule of thumb for determining lowest likely VMP of a string based on varying ambient conditions like there is one for estimating the highest VOC?
Use VOC to make sure you do not exceed your inverter's capacity. Panel VOC x number of panels in your string x 1.2 (a rough constant to adjust for cold weather voltage boost) should be less than your inverter's max DC input voltage rating.
Use VMP to make sure you meet your inverter's MPP startup threshold. VMP at highest rated ambient temperature (since voltage drops as temperature increases) x number of panels in your string must be equal or greater to your inverter's lowest MPP operating voltage range.
Use LSC to ensure you do not exceed your inverter's maximum current capacity, that is, the maximum amps your controller can take. So LSC x number of parallel strings (if you are just running one string of panels in series the lSC is as rated for a single panel) must be lower than your inverter's maximum short circuit input current.
Is this roughly correct? Setting aside sizing an array according to your energy needs etc., etc., are these three factors what you need to use to make sure your inverter has enough juice to charge your batteries while not going boom?
Thanks in advance!
P.S. Is there a rule of thumb for determining lowest likely VMP of a string based on varying ambient conditions like there is one for estimating the highest VOC?