Two 170 Ah 12V LiFePo batteries in parallel.
175 Amp Max continuous discharge
350 Amp Max Peak Discharge Current
300 Amp internal fuse
BMS has Over Current Protection
I have NO fuses or anything between the two batteries and my busbar. I have three circuits exiting the busbar. Each circuit has a bolt on terminal fuse (Blue Sea MRBF Terminal Fuse Block): a 300 Amp fuse between my busbar and 2200 Watt inverter, a 50 Amp fuse between my charge controller and the busbar, and a 150 Amp fuse between my 12 V fuseblock and my bus bar.
Obviously, if all circuits were maxed out, I could have a situation where the cumulative ask is higher than the combined 350 Amps of continuous discharge. Based on my intended usage, this will never happen (famous last words I'm sure). My 12 circuits off the fuse block will likely never exceed 50Amps ( I put the large fuse on because I'm using large copper than necessary. ), the charge controller isn't "supposed" to be a load (but maybe it is in some fault cases?), and the inverter will only draw anything near the full 300 Amps when I turn on a very high consumption cooking appliance that I intend to only have in use for 20 to 30 minutes a day maximally.
1) Is this bad design? Should I do something different? Put smaller fuse on the DC fuse block that puts a hard limit on my intended low loads from that branch?
2) What exactly would happen if I managed to ask my batteries for the full load of 400 or 500 Amps? BMS shuts down the batteries, correct?
Open to all suggestions and advice
175 Amp Max continuous discharge
350 Amp Max Peak Discharge Current
300 Amp internal fuse
BMS has Over Current Protection
I have NO fuses or anything between the two batteries and my busbar. I have three circuits exiting the busbar. Each circuit has a bolt on terminal fuse (Blue Sea MRBF Terminal Fuse Block): a 300 Amp fuse between my busbar and 2200 Watt inverter, a 50 Amp fuse between my charge controller and the busbar, and a 150 Amp fuse between my 12 V fuseblock and my bus bar.
Obviously, if all circuits were maxed out, I could have a situation where the cumulative ask is higher than the combined 350 Amps of continuous discharge. Based on my intended usage, this will never happen (famous last words I'm sure). My 12 circuits off the fuse block will likely never exceed 50Amps ( I put the large fuse on because I'm using large copper than necessary. ), the charge controller isn't "supposed" to be a load (but maybe it is in some fault cases?), and the inverter will only draw anything near the full 300 Amps when I turn on a very high consumption cooking appliance that I intend to only have in use for 20 to 30 minutes a day maximally.
1) Is this bad design? Should I do something different? Put smaller fuse on the DC fuse block that puts a hard limit on my intended low loads from that branch?
2) What exactly would happen if I managed to ask my batteries for the full load of 400 or 500 Amps? BMS shuts down the batteries, correct?
Open to all suggestions and advice