Don't use automotive cables, fuses, or busbars for 48V systems.
Be wary of inexpensive DC breakers on Amazon.
YES
Doing this as a hobby is fine, but don't expect any ROI.
Victron rules!
I do expect power when the grid is down - that is priceless - that was my top 3 goals
"Its the features I need, not the money I spend that matters most"
I never expected ROI, but I still was careful. I planned and hit about 80% of design targets upon implementation, the other 20% was replacement products or rewire work. Not bad IMHO
26 years of systems, that grew over time, from $5 a watt panels to today
The system I built, that I have now, cost in parts is about $30,000 and DIY work
70kwh of batteries
2nd generation of panels - 20 of the 32 were free - 4 250w + 28 305w to 375w -
NEED MORE
4th generation of battery - lead acid (3 types) to DIY Tesla Model S
4th generation of inverters - 12v ??? to 24v Trace to 48v Xantrex to XW Pro
3rd generation of CCs - PWM to RV MPPT to Conext MPPT
mostly same AC and DC wiring and conduit, and mounts
NOW I am replacing my main AC panel with a 200 amp - aim for this.
Was 60 amp service, now 125 amp service, will be 200 amp service - someday
biggest mistake: I used PVC conduit for the 6 awg DC feeders from combiner to DC bus. At the time I was a 24v array and battery system. 30v and above needs metal conduit. When I switched to 48vdc based system, I now have on my queue replacement tasks for the PVC conduit on the 4 arrays
Wire size on your inverter OUTPUT should be large enough to handle your end result, other wise you will need to R&R the older smaller conductor.
Ask me how I know.
My CLP is now a 100 amp panel and is supplied now with #2 (115amp) copper from the grid (100amp breaker) and #1 (130amp) copper from the dual inverters to Transfer Switch and again #1 from TS to CLP. Not that long of a run, and #1 just feels better in that path.
Dual inverters can do 24,000 watts for 1 minute, which is 100 amps
If I go 3 inverters, which will require some custom rewiring to place the unit, they can do 36,000 watts for 1 minute, which is 150 amps. that conductor path should be fine, as that is definitely an upper limit I will not try to reach and the inverters would shut down. the conductor is THWN-2 and for 90Deg C, can support 150amps
Today, I would install the Boss siblings for 200 amp on a new install, but not this house
,
Lastly,,
- print out Table 310.16 and keep it close to your heart, and usually follow the 75Deg C column
- get the latest NEC, tab it and search it
- utilize Mike Holt guides and videos
- watch Ryan Jackson videos
- watch Mayfield videos
- watch Electrical Code Coach videos
- continue to learn