so you guys convinced me to do an inverter/charger with batteries instead of generator for well pump backup.
as a refresher its a 1hp pump that draws 22-25 amps startup and 9 amps run.
leading contender has been the growatt 6000. its low frequency so it wont have any problems starting the pump. it will only be used for emergencies.
so why am I now reading this (on watts247)and what the heck does it mean? and does it affect all 240v inverters with an autotransformer? educate me
We no longer sell any units MPP/ Growatt or any other brand having (built in) or requiring an Auto Transformer on the output, If the inverter is in bypass mode, any Grid Imbalances will be fed through the inverter Auto Transformer
In some cases up to 60A has been seen
Even worse when more auto transformers are put in parallel, with some models.
as a refresher its a 1hp pump that draws 22-25 amps startup and 9 amps run.
leading contender has been the growatt 6000. its low frequency so it wont have any problems starting the pump. it will only be used for emergencies.
so why am I now reading this (on watts247)and what the heck does it mean? and does it affect all 240v inverters with an autotransformer? educate me
Growatt 48V 6000T 6kW MPV (250V Solar Input) We no longer support this model due to potential Autotransformer issues feeding back to Utility.
We no longer sell any units MPP/ Growatt or any other brand having (built in) or requiring an Auto Transformer on the output, If the inverter is in bypass mode, any Grid Imbalances will be fed through the inverter Auto Transformer
In some cases up to 60A has been seen
Even worse when more auto transformers are put in parallel, with some models.