I believe Victron LF inverters do have user setting for maximum AC input current allowed. (load shaving)
Charging from AC input will be limited by charger parameter settings or maximum AC input allowed.
When AC output exceeds user set AC input limit, AC output will be supplemented by battery power through inverter. This is great for smaller generator operation.
AC output load has first priority on limited AC input power. As AC output load increases there will be less overhead AC input power available for battery charging. This is a smooth transition from charging battery to drawing from battery to support greater AC output loads.
The AC output load can exceed what generator or inverter is capable of individually by combining power from both sources.
There is a small response time in the order of 10-20 msecs for AC output surge loads before inverter/battery picks up any excessive AC output surge load current. This can cause generator to momentarily bog down from momentary surge current, causing a shift in its AC frequency output, which causes inverter to release from generator. As long as inverter can support AC output load, the inverter will not shut down for overload and the inverter will resync and reconnect to generator again after a 20 sec to minute gap.
Charging from AC input will be limited by charger parameter settings or maximum AC input allowed.
When AC output exceeds user set AC input limit, AC output will be supplemented by battery power through inverter. This is great for smaller generator operation.
AC output load has first priority on limited AC input power. As AC output load increases there will be less overhead AC input power available for battery charging. This is a smooth transition from charging battery to drawing from battery to support greater AC output loads.
The AC output load can exceed what generator or inverter is capable of individually by combining power from both sources.
There is a small response time in the order of 10-20 msecs for AC output surge loads before inverter/battery picks up any excessive AC output surge load current. This can cause generator to momentarily bog down from momentary surge current, causing a shift in its AC frequency output, which causes inverter to release from generator. As long as inverter can support AC output load, the inverter will not shut down for overload and the inverter will resync and reconnect to generator again after a 20 sec to minute gap.