I have 4 Dokio 410w panels. I want to charge my Ecoflow Delta Pro. The max voltage the Delta Pro can accept is 150V. I believe the Delta pro can accept a maximum charge current of 15 amps.
According to the panel specs, the maximum power voltage is 31V. The maximum power current is 13.09. So 31 x 13.09 =405.79. By that alone, 4 panels in series would give me 1623 watts.
I’ve asked this question in other forums, and have golden the same answer. I should not string 4 of these panels in series to the Delta Pro because the Voc = 37.08 and 37.08 x 4 =148.32. Right at the 150V limit. Keep in mind I’ll be connecting the panels with at least 100’ of 10 AGW cable, so there will be a few volts of loss. I live ln Orlando so it almost never gets below freezing. So maybe the Voc won’t get much higher?
So what is the real risk of a 4S connection? What should my Voc safety margin be? I don’t want to ignore advice just because I don’t like the answer.
According to the panel specs, the maximum power voltage is 31V. The maximum power current is 13.09. So 31 x 13.09 =405.79. By that alone, 4 panels in series would give me 1623 watts.
I’ve asked this question in other forums, and have golden the same answer. I should not string 4 of these panels in series to the Delta Pro because the Voc = 37.08 and 37.08 x 4 =148.32. Right at the 150V limit. Keep in mind I’ll be connecting the panels with at least 100’ of 10 AGW cable, so there will be a few volts of loss. I live ln Orlando so it almost never gets below freezing. So maybe the Voc won’t get much higher?
So what is the real risk of a 4S connection? What should my Voc safety margin be? I don’t want to ignore advice just because I don’t like the answer.