I am in the planning stages for my solar system form my Tiny house. i have already purchased my Growatt 3000w 24V all in one units.
Due to the design of the house roof the plan was to put 3 panels on each side. I had looked at Trina 400 W panels but if i did the math correctly they would be to much for the MPPT charge controller. I also found some REC 350 watt panels that I think will work.
Growatt
Max PV array = 2000W
MPPT Range = 30VDC - 115CVDC
Max PV OCV = 145 VDC
Maxium Solar Charge Current = 80 A
Trina panels
Rated power = 350W
Open circuit VOC = 45.4
Max Voltage (VPM) = 41.1
Short Circuit Current = 10.18 A
Max Power Current = 9.74
Max System voltage = 1500 VDC
Fuse Rating = 20 A
REC Panels
Rated power = 350W
Open circuit VOC = 46.7
Max Voltage (VPM) = 38.9
Short Circuit Current = 9.27 A
Max Power Current = 9.0
Max System voltage = 1500 VDC
Fuse Rating = 20 A
With both I think i would have to wire in series. Going in parallel would be over the Fuse rating if i understand where that comes in correctly. The short circuit current would be almost 30A.
With the REC panels in series i would have VOC=140.1 and VPM=116.7 Current would remain at 9A. This is slightly over the 115. Is that ok?
With the Trina panels I would be at VPM=121.3
I am thinking i would be better going with the REC panels. I have attached how I plan to wire everything. Any thoughts or suggestions are welcome.
Due to the design of the house roof the plan was to put 3 panels on each side. I had looked at Trina 400 W panels but if i did the math correctly they would be to much for the MPPT charge controller. I also found some REC 350 watt panels that I think will work.
Growatt
Max PV array = 2000W
MPPT Range = 30VDC - 115CVDC
Max PV OCV = 145 VDC
Maxium Solar Charge Current = 80 A
Trina panels
Rated power = 350W
Open circuit VOC = 45.4
Max Voltage (VPM) = 41.1
Short Circuit Current = 10.18 A
Max Power Current = 9.74
Max System voltage = 1500 VDC
Fuse Rating = 20 A
REC Panels
Rated power = 350W
Open circuit VOC = 46.7
Max Voltage (VPM) = 38.9
Short Circuit Current = 9.27 A
Max Power Current = 9.0
Max System voltage = 1500 VDC
Fuse Rating = 20 A
With both I think i would have to wire in series. Going in parallel would be over the Fuse rating if i understand where that comes in correctly. The short circuit current would be almost 30A.
With the REC panels in series i would have VOC=140.1 and VPM=116.7 Current would remain at 9A. This is slightly over the 115. Is that ok?
With the Trina panels I would be at VPM=121.3
I am thinking i would be better going with the REC panels. I have attached how I plan to wire everything. Any thoughts or suggestions are welcome.