Today in “I should know better”, I’m running through some tests in a [remote] cabin setup. I’ve been on here learning long enough to have a lot of confidence in the end-state. But I may have some less-than-ideal temporary scenarios as I get things ready to be configured for the long-term.
For reference, this is close to the end-state (plus all the appropriate ground runs, etc.)

Currently I only have the “XP Sub” wired up locally in the PV shed (which is attached to the side of the cabin). Inverter is feeding this panel and some local outlets for testing. I have a 6AWG bare copper wire running to the “House Main” for grounding, which is grid service entry currently (“Grid Main” is not in place yet) and is N/G bonded.
As-is, the “XP Sub” is NOT N/G bonded and has dedicated neutral and ground bars for termination.
The question(s):
- Is it kosher to ground the XP Sub panel (temporarily) this way?
- should the XP Sub be bonded locally since it’s technically not configured as a sub panel yet?
- if ^yes^ can it be bonded while still grounding via the main panel?
- what else should i know?
My backup plan was to install a grounding rod next to the shed, ground the panel there, and bond N/G locally…but ran out of time. I will repeat that this is a TEMPORARY setup while I get all my things in order.
Don’t yell at me. Thanks in advance!
For reference, this is close to the end-state (plus all the appropriate ground runs, etc.)

Currently I only have the “XP Sub” wired up locally in the PV shed (which is attached to the side of the cabin). Inverter is feeding this panel and some local outlets for testing. I have a 6AWG bare copper wire running to the “House Main” for grounding, which is grid service entry currently (“Grid Main” is not in place yet) and is N/G bonded.
As-is, the “XP Sub” is NOT N/G bonded and has dedicated neutral and ground bars for termination.
The question(s):
- Is it kosher to ground the XP Sub panel (temporarily) this way?
- should the XP Sub be bonded locally since it’s technically not configured as a sub panel yet?
- if ^yes^ can it be bonded while still grounding via the main panel?
- what else should i know?
My backup plan was to install a grounding rod next to the shed, ground the panel there, and bond N/G locally…but ran out of time. I will repeat that this is a TEMPORARY setup while I get all my things in order.
Don’t yell at me. Thanks in advance!