12V 200 Ah bus bars span 2 cells in series, 4 in parallel. GFB 100Ah cells
I think this is saying that the battery post size is M6.
So here's my question...
I want to use as large a conductor from the battery post to the T-class fuse for positive and over to the victron shunt for negative.
I think the correct lug would be a 1/4 SAE size Selterm or equivalent lug.
I see Selterm sells a AWG 6. non-affiliate link to amazon US page with it:
Ancor sells one 'marine grade' up to 1/0 AWG:
I only need to run 2 feet lengths of both.
while running 150 A to 200 A consistent with my pool pump setup is highly uncommon except for the tests I'm performing on the BMS, right now the only thing getting warm in my setup are the conductors in this location between the battery cells and the t-class fuse and the shunt.
The wire selection chart here:
suggests that I should be running 1 AWG (150A) to 2/0 AWG (200A) conductors..
1/0 is larger than 1 AWG, but not as large as 2/0 AWG.
I think - may be wrong - that 1/0 is commonly called 0 AWG?
AI tells me:
Copper wire
At 75°C, 1/0 copper wire can carry 150 amps with insulation types like THHN/THWN-2 and RHW
At 90°C, 1/0 copper wire can carry 170 amps with insulation types like XHHW-2 or USE
Battery cable
1/0 battery cable can carry up to 250 amps
Is that accurate?
The wire I was looking at is a favorite here - the windy nation welding wire:
Though to be honest I don't see an amperage or current rating except up to 600V. The close up pictures they provide are for 4 AWG cables, not the 1/0.
battery spec sheet below/attached.

I think this is saying that the battery post size is M6.
So here's my question...
I want to use as large a conductor from the battery post to the T-class fuse for positive and over to the victron shunt for negative.
I think the correct lug would be a 1/4 SAE size Selterm or equivalent lug.
I see Selterm sells a AWG 6. non-affiliate link to amazon US page with it:
Ancor sells one 'marine grade' up to 1/0 AWG:
I only need to run 2 feet lengths of both.
while running 150 A to 200 A consistent with my pool pump setup is highly uncommon except for the tests I'm performing on the BMS, right now the only thing getting warm in my setup are the conductors in this location between the battery cells and the t-class fuse and the shunt.
The wire selection chart here:
suggests that I should be running 1 AWG (150A) to 2/0 AWG (200A) conductors..
1/0 is larger than 1 AWG, but not as large as 2/0 AWG.
I think - may be wrong - that 1/0 is commonly called 0 AWG?
AI tells me:
Copper wire
At 75°C, 1/0 copper wire can carry 150 amps with insulation types like THHN/THWN-2 and RHW
At 90°C, 1/0 copper wire can carry 170 amps with insulation types like XHHW-2 or USE
Battery cable
1/0 battery cable can carry up to 250 amps
Is that accurate?
The wire I was looking at is a favorite here - the windy nation welding wire:
Though to be honest I don't see an amperage or current rating except up to 600V. The close up pictures they provide are for 4 AWG cables, not the 1/0.
battery spec sheet below/attached.