Wire gauge for DC
jamesnewman01377
I need a little help, I'm a beginning so bear with me. I have 6 solar panel wired in series to a switch, from the switch to the Growatt inverter is about 130 feet, how do I now what gauge wire do I run for DC, the panel are 250w, 37.6v open circuit, VMP 30.3, at 8.27 amps, in series (if my math is right) that would be 225.6v an 8.27 amps, thanks, James
sunshine_eggo
Happy Breffast!
USA
You start with cable that can handle the current.
Then you use a voltage drop calculator to determine % voltage drop, which equates to % power lost.
Click estimated resistance tab and plug in the numbers (use Vmp and Isc):
10awg can more than handle 8.27A, and it only has a 1.18% voltage drop - anything less than 3% is pretty great.
Even 14awg would be just under 3%.
smoothJoey
Hoop Dee Doo!
How far from the switch to the panels?
jamesnewman01377
I asked about the distance between the switch and the panels.
I’m sorry, I would say 15 foot, the panels are mounted on a roof of a dock building and the switch is mounted just under the roof line.
smoothJoey
Hoop Dee Doo!
14 awg would be just under 3% voltage drop.
10 awg would be a little over 1% voltage drop.
jamesnewman01377
Thank you.
smoothJoey
Hoop Dee Doo!
What’s the difference between AWG and THHN wire?
AWG is the measure of the conductor's diameter.
THHN is a type of wire. THHN is useful wire but it is not suitable for your application.
The insulation on THHN is not designed for exposure to the sun.
You need wire specifically meant for your application.
jamesnewman01377
I meant the wire between the switch and the inverter, it will be in conduit.