This is tech cable, you guys will never deal with it, but I want to explain something..

Sometimes I have to wire up a 600 volt motor and its always a lot of trouble to pull multiple armoured cables like this.
So sometimes ( when the planner is on the ball ) he will order tech with all the wires in need in it.
It will have the three power conductors and bond of course and three control wires for control ( seems pretty obvious )
Other times I will use another tech cable with identical wires 3, 4, 7 , 9, 12....
All these wires are rated for 600 or 1000 volt and this is perfectly except able.
I can run 600 with 24 vdc control or automation inputs all kinds of things.
This is allowed!
BUT you need to be very careful.
Sometimes induced noise will cause some problems.
This is not a code problem this is a noise problem.
I would not run a Modbus cable in a conduit with anything thats going to generate RF like an inverter or MPPT controller.
But everything else is fair game
So in those rare cases I run separate cables or if Im using a conduit I will run a shielded cable and run it separate.
Maybe its different in the USA, but the majority of the time you buys spool of wire, its rated at 600 volt.
No issues...
But if it makes you feel better run more conduits.

Sometimes I have to wire up a 600 volt motor and its always a lot of trouble to pull multiple armoured cables like this.
So sometimes ( when the planner is on the ball ) he will order tech with all the wires in need in it.
It will have the three power conductors and bond of course and three control wires for control ( seems pretty obvious )
Other times I will use another tech cable with identical wires 3, 4, 7 , 9, 12....
All these wires are rated for 600 or 1000 volt and this is perfectly except able.
I can run 600 with 24 vdc control or automation inputs all kinds of things.
This is allowed!
BUT you need to be very careful.
Sometimes induced noise will cause some problems.
This is not a code problem this is a noise problem.
I would not run a Modbus cable in a conduit with anything thats going to generate RF like an inverter or MPPT controller.
But everything else is fair game
So in those rare cases I run separate cables or if Im using a conduit I will run a shielded cable and run it separate.
Maybe its different in the USA, but the majority of the time you buys spool of wire, its rated at 600 volt.
No issues...
But if it makes you feel better run more conduits.