difranco999
New Member
I'm looking at placing solar in an open field that's about 300' from our house. The panels will be on a ground mount, and there will be an insulated shed to house the inverter and batteries. Currently looking at using a EG4 1200xp (spec list for quick reference).
In the diagram below you can see a rough idea of what I'm envisioning.
My primary question right now is if my AC wire size calculations are correct. Also interested in general feedback as to whether this design makes sense or if there's a better way.
I used this wire size calculator... Plugged in 300' @ 50 amps w/ 3% voltage drop, it reported back 3awg.
For the ground wire, I used this calculator which reported 10awag.
So in summary, I would need 5 separate 500' runs of 3awg wire:
Wire 1: L1 from house to inverter
Wire 2: L2 from house to inverter
Wire 3: Neutral from house to inverter
Wire 4: L1 from inverter to house
Wire 5: L2 from inverter to house
And 1 500' run of 10awg wire for ground
Is this accurate?
In the diagram below you can see a rough idea of what I'm envisioning.
My primary question right now is if my AC wire size calculations are correct. Also interested in general feedback as to whether this design makes sense or if there's a better way.
I used this wire size calculator... Plugged in 300' @ 50 amps w/ 3% voltage drop, it reported back 3awg.
For the ground wire, I used this calculator which reported 10awag.
So in summary, I would need 5 separate 500' runs of 3awg wire:
Wire 1: L1 from house to inverter
Wire 2: L2 from house to inverter
Wire 3: Neutral from house to inverter
Wire 4: L1 from inverter to house
Wire 5: L2 from inverter to house
And 1 500' run of 10awg wire for ground
Is this accurate?