I just received my Sok Batteries I’m going to wire four of them in parallel with a 3000 W inverter. Sok said use four gauge wire with a 300 amp fuse. The inverter calls for 4/0 wire 350 amp fuse. I’ve done a handful Battleborn installs and I know they don’t want you using 4/0 wire they want you using 1/0. so my question is can you pull 300 A through four gauge wire and does a 300 amp fuse going to protect four gauge wire?
 
I just received my Sok Batteries I’m going to wire four of them in parallel with a 3000 W inverter. Sok said use four gauge wire with a 300 amp fuse. The inverter calls for 4/0 wire 350 amp fuse. I’ve done a handful Battleborn installs and I know they don’t want you using 4/0 wire they want you using 1/0. so my question is can you pull 300 A through four gauge wire and does a 300 amp fuse going to protect four gauge wire?
This is what I use:


4 gauge wire is undersized and should not be fused at 300 or 350 amps. The fuse is to protect the wires, and it won't.
4/0 is not 4 gauge, it's 0000 gauge.
 
3000 ac watts / .85 conversion factor / 12 volts low cutoff = 294.117647059 service amps.
294.117647059 service amps / .8 fuse headroom = 367.647058824 fault amps.
That means a 350 amp fuse and wire rated > 350 amps.
You want the fuse to protect the wire not the other way round.

 
3000 ac watts / .85 conversion factor / 12 volts low cutoff = 294.117647059 service amps.
294.117647059 service amps / .8 fuse headroom = 367.647058824 fault amps.
That means a 350 amp fuse and wire rated > 350 amps.
You want the fuse to protect the wire not the other way round.

Exactly what I thought
 