It is a pretty common practice in manufacturing to run parallel conductors, where one large conductor creates problems/challenges. If you think the practice needs to be discouraged, please state your position.It is a bad idea to "parallel wires to increase wire gauge"
Parallel conductors are used *all the time*, especially in industrial electrical. Several different factors drive that decision, but often it’s just conductor availability, equipment size, ease of installation, etc.It is a bad idea to "parallel wires to increase wire gauge"
Exactly. That is why if you parallel 3 wires you don't go for 3 times the max current a single wire can handle. IIRC the number was 80% of the max current when wires are in parallel. But still - the job must be done correctly to avoid overloading a single wire.There will never be equal resistance on each paralleled wire, each could haul uneven loads. Not bad for the light load wire, but the heavy load wire may object and return all your smoke.
Each wire must be fused to that single wires ampacity. Else, in many scenarios one wire could carry its overload.
Correct its done all the time and not any issues. AC or DC its all the same.Parallel conductors are used *all the time*, especially in industrial electrical. Several different factors drive that decision, but often it’s just conductor availability, equipment size, ease of installation, etc.
Charger like this? It has 100v max PV input. If you have 4 panels, you could do 2 series and 2 parallel, bring in about 16 amps at 76v on a 10ga wire and be done with it.I’m confused I have 4 240 watt panels (specs attached) in parallel would give me about 38 volts and about 32amps I have a rvr-40 renogy (specs attached) should that work
Not a requirement but your max power to the battery would be the rated watts. What is your battery system voltage?Will I need 2 charge controller since since the max solar input power is 520
So with that 40amp charger, you could charge with 520w max at any time. It is common to have more panel watts than what you can use allows for good current on less than perfect conditions. But if you need to put more than 40amps to the batteries, you need a larger charger or a second charger.12 volts