jeff.lankford
Solar Enthusiast
As I tried to explain above, you don't need a separate feeder tap "device" or box. I made my tap inside the manual transfer switch enclosure using dual lugs. Look carefully at my simplified diagram and the photo of the inside of the MTS.So a question; does the feeder tap needs to connect to the manual transfer switch? the diagram only shows one line connecting the feeder tap and manual switch, so I am not sure if that mean cable connection. If that is the case, then I will most likely place the manual transfer switch beside the inverter so it can also get the cable through the same hole from the feeder tap.
There are several versions of the EG4 wiring diagrams. Which one are you using for the "whole house backup with feeder tap" diagram"? I prefer the version I attach here, but as I explained above, I have omitted the feeder tap and feeder tap breaker from my installation - the meter/main connects directly to the MTS grid/line input lugs (the lugs that I replaced with dual lugs).

No, as explained above, if you add a main breaker to your main panel. According to your photo, your main panel does not contain a main breaker. In the photo I've attached, there are only main lug connections inside the area I circled. You should be able to find a main breaker option for your main panel and install it. As I explained above, if you do that then a separate feeder tap breaker is not needed. It appears your panel is a Square D model. This link gives you an example of the main breaker that could be mounted in the area I circled. Please note this is ONLY an example. Your electrician needs to determine the exact model of main breaker that would be needed for your panel.The feeder tap breaker......do i need this...in my main service breaker, does it not contain a 200amp breaker? I will try and draw how I understand my connection should be and share it here later today. Thanks

Yes, that's correct. You can run a complete new cable from the MTS load lugs to the main breaker panel input. The existing output from the meter/main will be disconnected and that output runs to the MTS line input lugs. In my case, it was easier to keep my existing cable to the main panel and splice an extension on it to let it reach the MTS, but that was to avoid running an entirely new cable to the main panel. Depending on where you mount your MTS, an entirely new cable might make more sense for you.@jeff.lankford some questions that came to my mind:
1) when all the connections are completed, the only power grid cable that goes to the main breaker panel should come from the manual transfer switch. If this is yes, the existing power grid connection that comes from the main server breaker will be removed?
Yes, that's what I've explained already with the splice (not a tap) I made in the meter/main to extend the existing cable. Your layout will depend on where you mount each device. I preferred everything to be on the outside of the house, so I didn't disturb/change anything regarding the inside main panel and the wiring going to it.2) If the existing power grid cable needs to be removed, instead of removing it, can I tap it to connect to the Manual transfer switch, that way I avoid having to do anything in the main breaker panel? I'm just trying to avoid touching existing connection and just use existing cables/connections as much as possible. But, the question would be if the cable they use for it will work with the manual transfer switch.
Please let me know, thanks!