Sorry, I write novels to explain things and why I do things
This is the Victron install guide recommendation for fuse and wire size
View attachment 277621
Which version do you have?
The size of the class T used should be 300amps or 400amps, you
Changed the breaker size from the PV panels to more closely match the MPPT - 40amp verse 60amp
Fuse to the buck converter - I would switch to this type breaker verse the automotive breaker -
Automotive breakers that self reset like the ones you picture can cause problem because you don't know if it is tripping and resetting - no indication ... I much prefer something I have to flip back so I know to watch for problems.
Both of these layouts require 4 bus bars to avoid stacking lugs. -- if you want to make changes - download drawio and use the two attached files ... it takes about 20 minutes on youtube to learn the basics.
Those are 200amp MRBF fuses to go onto your battery post - or you can put them at the bus bar end of things. They require a holder.. I say the bus bar end because I haven't seen a picture of the battery and if it has terminal lugs the output cables are connected to or if you are just bolting directly to the positive cell and the BMS. Terminal lugs is for sure the way to go on that.... safer and the MRBF can't hurt anything if you torque it down to spec.... I get mine from pkys.com or mouser... There are many cheap copies on amazon that don't stand up to actual use...
One thing I see that is missing is an equalizer to run on each string to keep the 2 batteries in sync - being home built and you can monitor the cells for runners that may not be an issue the typical new user with store bought batteries would need to add one.
The plastic enclosure you have on the table will hold both of the dihool black breakers
Note - on the bus bars I picked the particular stud things connect to on purpose
And here it is with the additional large MCCB instead of the switch -- gives you a single switch to turn off the batteries... a second switch to turn off the MPPT... and a third switch to kill power to the buck converter and DC panel.
The advantage of the MCCB is you can turn it off while there is a full load on it with no damage -- the standard switch in the first drawing is only meant to be turned off while there is no load. If turned off repeatedly with a load the contacts get burnt and it starts running hot.
I am assuming the AC out has a fuse or breaker built into the existing panel as does the DC panel. If they don't have that something would need to be added.