Zero voltage after branch connector.

Cmorgan4

New Member
Joined
Jul 2, 2021
Messages
1
3/1 branch connectors in parallel panel configuration went .03 voltage while on a trip and the controller showed night mode 0amps 0watts. Unplugged the branch connectors and plugged one panel into the controller and have power. If one of the three panels went bad, could it back feed power from the other two panels and cause a zero voltage condition at the branch connector? I bought replacement connectors and have the same zero voltage issue so I’m assuming one of the panels is bad. Can’t find any references to this problem online. Have run the system two years problem free.
 
Welcome to the forum.

Remove branch connector
Connect only panel 1 - do you have power?
Connect only panel 2 - do you have power?
Connect only panel 3 - do you have power?
Install branch connector - do you have power?

The above steps should allow you to isolate the problem component.
 