  1. A

    Is my system safe?

    I ran the 2000w inverter on the edge of its ability and as much 12v stuff I could find, shunt was showing the system touching 2.2kw at times and after an hour the hottest temp I could get my cheap temp gun to read was 156F directly on the fuse.
  2. A

    Is my system safe?

    Thank you, what would you improve?
  3. A

    Is my system safe?

    Also upgraded to blue sea anl fuse and holder recently that another member suggested.
  4. A

    Is my system safe?

    Lots of good info, thank you. Shelf is made of 1x12 pine that I stained. Cement board is not a bad idea, I will consider redesigning my shelf but I really hope to keep things safe with proper sized wire and fusing. The buss bars are 600a rated. Skar audio, pic below, have not filed to...
  5. A

    Is my system safe?

    Code like that is way over my head, I’m very mechanically inclined and familiar with 12v stuff from the automotive world but expert electricians blow my mind lol. I did run about a 45 minute test pulling at least 120a the entire time, averaged 140a, saw spikes at 180a with the battery bank...
  6. A

    Is my system safe?

    I didn’t know about the 2 different types of fuses, should I be using the ann over an anl?
  7. A

    Is my system safe?

    Does that include lower amperage breakers?
  8. A

    Is my system safe?

    Will definitely have to try that! What is the mrbf?
  9. A

    Is my system safe?

    That is something else I had thought about doing is ordering a name brand quality anl fuse but I didn’t think that would be the answer to everything. Are there any breakers up to this task? I really like being able to use them as on off switches if current is low. Someone else mentioned the...
  10. A

    Is my system safe?

    I have gone over my connections many times, that was my first thought too. I was using a space heater and variable heat gun so I could dial right up to the limit of the inverter to test for things like this. They ran for a half hour or so pulling 150-170a
  11. A

    Is my system safe?

    Yes, the breaker did get warm also. Is there a cooler safer way to have short circuit protection?
  12. A

    Is my system safe?

    This is the tool I’m using to crimp, running it down with an impact, not by hand. My inverter is 2000w. I am aware my one 250w panel isn’t enough, that is why I made sure to show that it’s a 50a charge controller dc-dc with mppt. I’ll have plenty of charger left for 3, maybe 4 panels in the...
  13. A

    Is my system safe?

    I would say the most this system would ever see continuous would be around 200a, saw Will’s video that recommended fuse/breaker 1.5 times expected continuous and to go up if there’s nothing directly at your calculation. The small white/black is 8ga from my charge controller and has a breaker...
  14. A

    Is my system safe?

    Yes I definitely plan to cover them, keeping the switch off for now when I’m not testing. I have double and triple checked for loose connections, that was my first thought. I was using a variable heat gun and space heater to keep it just under tripping my inverter, not a real world scenario...
  15. A

    Is my system safe?

    It is a 2000w pure sine from harbor freight. I should have included that, thank you!