Ok so this is what i found if anyone else is a newbe and concerned connecting the bigger inverters ...
Apparently for a 48v INV you need a 10w 470 ohm resistor to precharge the INV before the full connection
to the batteries ... or a 240v 100w light bulb : )
Thanks for the link 420.
Looking for advise on the correct flexible cable from the shore power outlet to my sunpowergold 6000w INV
obviously for max charging for the batteries (jackiper 48v 5.1 x2)
Also as it has a transfer switch built in what cable should i use to connect to the ac out (inverter) and into a big...
Guys I’m looking at adding a GT4000 opti solar inverter to my system .. it’s a grid tie but I’m wanting to connect it to the AC in of my growatt es500’s as a ‘generator’
Thus maximizing the draw from the GT’s constant AC output.
Presumably I can set the GW function to ‘grid first ‘
Any reason...
Hey Guys flashing light on circuit board of growatt es5000- no fault codes ??
Only issue i can see is incoming amps should be 8.0 .. often just seeing 0.1 ??
When i shut down and power up ill see 8a but gradually drops off?
Intermittent cloud ( voltage reading good )
Connected to jakiper 5.2 48v
It was suggested on a FB solar group that i should go with 2s6p for 70a .... apparently that is the most powerful ?
I heaven't heard that before as the KWh remains the same... and more crucially i don't have 50' of 2/0 wire lying around
I have 2 Gw 5 AIO .. but have an opportunity to pick up the GT4 very reasonably.... So I took a look at this thread as advised.
https://diysolarforum.com/threads/can-growatt-spf-5000es-handle-ac-coupling.76673/
So the grid tie inverter has to see a constant 220, presumably that's why they go...
Thankyou Michael .. esp the comment on SE facing panels ... experience experience.. I already have the sungoldpower 6k but it is not a solar off grid. I'm unable to add panels directly to it hence the Charge controller. I'm guessing if i expand bigger i'll at a growwatt inv or something similar...
Hi Guys i had promised to give some feedback so here it is ....
Mistersandals estimate " Total on paper: 3104W" was pretty fair considering the 1st string points south and the second points
west with 1 panel south facing ... they are also set at 51' (from memory) which was the optimum at...
2S3P = Ok so that's 3 wires going into the SCC ... the victron (for argument sake) has only 1 inlet for PV so i'd need a combiner ? Other than the wifi BT options with the victron is there any reason they are so expensive .. they look cheap (manufactured in china?) i know people rave about them...
Hey any comments on the components i'm considering here... will be expanding to another battery in a month or two
and obviously adding panels when funds enable me to .... (solar charge controller too small?)
Please suggest optimal config of panels
Hey Guys
Wondering if someone has used the es5000 just to charge battery modules from utility?
Been through the options 001 Listed here....I'm guessing the real question is this..
Q. Is Battery charging ever considered a LOAD?
SOL
Solar firstSolar energy provides power to the loads as first...
Thank you , No restrictions on connecting the panels to the most efficient output.
Max Mppt Op Voltage = 450vdc
Max PV input 6000w
Max Charge 100a
AIO growatt 5000es
270w panels vmpp=36v - ISC= 7.9a
375w Panels vmpp =40v - ISC= 9.9a
Thanks for your patience and input .. very likely going to get the growatt 6k so my diagram looks like this
now ... 3S2P.
Is this looking ok for the charger input and amps etc
Next big question is wire size from panels ? Will it be just 10awg?
My run will be 30ft max and i tried to use the volt...
Guys
Just about to put the panels on my new array rack.
Please chime in on panel configuration .. I’m planning
On
12 x 400w all in series
400/31v(vmp) = 12.9a(imp)
12x 31v = 372v (under my MPPT LIMIT of 450v)
Fused at 15a
Any draw backs to this over
6s2p ?
I HAVE NO SHADE ISSUES
Thanks!
I was talking about the solar charge controller ... I think i'm going to save the sungold power 6k INV for another project and buy a growatt 6k AIO or the EG4 6.5 120v single phase .. both are 1299 but include a huge input MPPT .. why pay a grand for the big victron charge controller ...
Guys ..
Can i use a EG4-LifePower4 Lithium Battery | 48V 100AH
AND
A Jakiper [PRO] Lithium Battery | 48V / 100Ah | 5,120wH
Connected in a server rack ??
Hey Guys
I want another string and have been advised on another forum that the voltage difference is too much
1 string of 270w x4 (1080w) panels in series
4x43.6voc = 174.4v.
1080/174.4=6.19a
And
1 string of 375w x6 (2250w)in series
6x48.8voc= 292.8v
2250/292.8= 7.6a
What are the guidelines...
That's Great!
So to summarize so i understand - Having 2 equal strings would net 2880w on paper
By adding one of the 375 to the smaller panels pushes that to 3104w
The volt difference is 16v ( is that an acceptable difference?) between the 2 strings
Sunshine can you explain the purpose of...
Hey i'm in a similar situation with a sunpowergold 6000w INV and a Jackiper 48v battery ... the battery is currently discharged to 12v do i need to connect the resistor between the batt and INV ? can i use the lightbulb?
Oh my ... I'm even more confused ? The battery(48v) has a current charge of 12v so well depleted ... can i not just connect my inverter to it (has an in built charger and get going?