I'm in the process of installing 34 Canadian Solar 380-watt panels on a ground mount. I'm using a Fronius Symo 10.0-3 208/240 string inverter. I have a 300 foot run from the inverter to my meter where the solar will line tap at the meter.
I have a ground wire that runs from the inverter to the...
The disconnect on the pole has a lug where the neutral comes in from the meter. That is where the ground wire is attached that then runs down the pole and into the "ground".
All,
I'm stuck on a grounding issue for my string inverter ground mount. I've built a 12kw ground mount array that is using a Fronius Symo 3-phase inverter that is 208-240. This is going to be a grid-tie system that will run directly to the meter with a line-tap. We are bypassing the...