Jenna, at Signature Solar was amazing getting to the bottom of multiple issues:
My 6000xp installed great, but the screws that secure the PV wires failed the 2nd time I used them (had to unhook all wires to test that a spare unit was ok). On 3 of the 4 terminals, they failed to clamp when the...
I'm using an LL-V1 as master with 2 Lifepower4s communicating with my 6000xp. The LL had to be primary/master & all batts had to be patched to their latest firmware.
Shouldn't all grounds be bonded into a single system with multiple rods to avoid ground loops? Would my understanding actually cause an issue because grounding solar mounts are an exception to the rule that I am unaware of?
I had the most bizarre road to getting mixed EG4-LL & Lifepower batteries to communicate with a new 6000xp... Only lead-acid mode would produce AC-Out at first. Flashing the firmwares didn't help. Finally we removed the LL, reducing the bank to just 2 Lifepowers, with all DIP switches down on...
@EG4_Jared Thanks for helping... Can you please share (or point us where to read) the details about:
* Battery wake up (not in manual or your pdf)
* Battery volt sample disable
* Start Quick Charge
* Force Discharge
* PV Isolation
In off-grid only use, is one or the other of the following...
Can SS PLEASE post publicly these settings & other support resources that SS has amassed? Many of us have Lifepower4s & Sol-Ark inverters & we need easy access to the info you only share off-line! ie: 'How to implement closed-loop BMS communications'... & now 'How to wake up drained EG4...
I'm assembling three 20a receptacles that will sit between 6 chargers and 3 of my generator's 4 120v outlets. The chargers will be wired to bus bars that are wired to the battery rack's bus bars.
I've loved Signature Solar, but had to walk away...
Why? - Over a month ago they asked me to send an email with my 6500EX questions. The most glaring one was: 'Why does page 7 of the manual cite both bad & ideal values for Total Harmonic Distortion of voltage, (regarding electronic-equipped...
Thanks for your input. If inverters are <3% typically, how can it be that page 7 of the 6500EX's manual not only lists that exact spec but it also (at the bottom of the page) cites <10% for non-linear loads (like PCs, TVs & other electronics). And, to top it off, Signature Solar says they...
I called Signature Solar with related questions and was told point blank to not hook up a low-cost, portable generator through any inverter. Unless you have proof your generator produces <5% Total Harmonic Distortion (THD), you risk frying sensitive electronics like the inverter (and if you're...
While there's little risk to introducing a good, solid bond while running, it is equally likely the software (that controls the battery-to-inverter communications) won't reset & "pick-up" on the fact that something has changed until you do. Thus my vote is power everything down, then bond the...
@jimT - correct... Previous success included no Earth ground, only a bonding between the various chassis. I don't think it matters what screw you use, though the screws intended for mounting to the rack should work just fine and should be quite safe to fiddle with. Good luck!