Hello, I am sorry if someone question that. I have solar system with - EASUN 5.5kw Hybrid Inverter MPPT 48V - 4x solar panels Suntech 440w - 4x Gel battery /12v 150ah/ - and Victron Energy SmartShunt 500A/50mV. When I ordered my inverter I ordered it with wifi module for monitoring. But before...
Thanks for fast answer. I will keep these setting, only I will change victron charged voltage from 52.8V to 56.2V.
And low cut-off voltage is enought at 48.0V?
In manual ask for 5.5kw inverter - Low DC Cut-off Voltage:
@load < 50% -->...
Hello, I am sorry if someone question that. I have solar system with
- EASUN 5.5kw Hybrid Inverter MPPT 48V
- 4x solar panels Suntech 440w
- 4x Gel battery /12v 150ah/
- and Victron Energy SmartShunt 500A/50mV (settings on smart shunt is by default only I have change battery amp to 150ah because...