  • Post in thread: Need To Add Arc Fault Detection to system

    They are on a separate rack, my issues is the structure I made to house the batteries and solar equipment is large enough to be considered a building. According to my inspector, this is enough to warrant needing arc fault.
  • Post in thread: Need To Add Arc Fault Detection to system

    I have a 3K Victron system (off grid with a generator as the backup) that is working very well. All components are Victron, including their Cerebro GX that provides very cool software for monitoring the system. I had it inspected by ESA and was told I needed to add Arc Fault and Ground Fault...
  • Post in thread: Need To Add Arc Fault Detection to system

    Ah interesting. So I might be able to push back on this then.
  • Post in thread: Need To Add Arc Fault Detection to system

    Here it is. Everything is working fine (in terms of the system is charging from the PV) with this wired in. I just can't tell if it is doing anything.
  • Post in thread: Need To Add Arc Fault Detection to system

    Nothing illuminated, but I just realized I had the inputs and outputs reversed. It's corrected, hopefully, I didn't fry it. I don't have RSD modules on the panels.
  • Post in thread: Need To Add Arc Fault Detection to system

    Just got a note from Schneider regarding my question on this: The MPPT Disconnect RS complies with NEC 690.11 "Arc-Fault Circuit Protection (Direct Current)", and includes an Arc Fault Detector. The MPPT Disconnect RS, when used in conjunction with the Conext MPPT 60 150 and Conext MPPT 80 600...
  • Post in thread: Need To Add Arc Fault Detection to system

    " PV source and output circuits " - the output circuits I assume to be charger controllers and inverter, which I do have in a small building. So I guess the question is, do both have to be on a building to require arc? If the output circuits are in a building, does this trigger the arc...
  • Post in thread: Need To Add Arc Fault Detection to system

    I am not able to find the power cable that came with this Schneider disconnect unit. It looks like that attached diagram. I posted a question on Amazon about getting a replacement, and got the following answer from Schneider...
  • Post in thread: Need To Add Arc Fault Detection to system

    Another option would be to lower the voltage. I could put my panels in parallel. According to the code, if they are less than 80V I don't need arc fault.
  • Post in thread: Need To Add Arc Fault Detection to system

    So you were right. I did get this hooked up using the labeling on the box. I got the lights, and like you predicted I got the blinking RSD light. But also as predicted in this thread, this unit will not disconnect if an arc fault happen without changing my MPPT controllers to Schneider ones...
  • Post in thread: Need To Add Arc Fault Detection to system

    From what I understand it just need to show the system has arc fault protection. As I was explained it need to show it can detect an arc fault and then protect the system in that event. My inspector seems pretty reasonable. If I could show the protection came from RDS, I think it would be fine
  • Post in thread: Need To Add Arc Fault Detection to system

    I have a ground mount. Which normally does not require arc fault. My issue is I built a structure for the equipment and batteries that is large enough to be considered a building (the structure I am powering in a bunkie and I didn't want to lose the space. One option is to make that structure...
  • Post in thread: Need To Add Arc Fault Detection to system

    Wow! This sounds promising. Thanks!
  • Post in thread: Using battery charger and solar charger at the same time

    I have a 12 V systems that is comprised of 2 6V deep cycles in series that are then wired in parallel to increase my capacity (4 6 V batteries in total with 230 Ah in each battery). My charger controller is the EPEVER 40A MPPT Solar Charge Controller and is hooked up to 4 100 W panels wired in...