Thanks RCinFLA, keepsake & 400bird.
Agreed if AC1 works AC2 should work but I’m off-grid. Some forums mentioned firmware bug kept AC2 from qualifying so I assumed that’s why & tested by switching to AC1. In my case neither AC1 nor AC2 qualified the generator.
I’m using same 11kw gen I’ve been...
Yes, Sandman. Thanks. No power on AC1. I have no grid access.
I have master-slave setup for the 2 XW’s. I think the setup works b/c the inverters communicate when pulling power from battery bank to power the house. I just can’t get master XW to qualify gen so I charge the batteries.
Thanks. Good idea re: min & max.
I do see voltage & frequency on status screen & yes it does say qualifying.
Good to know re: build.
Ok. I’ll open a tech support ticket.
Feedback from you is helpful. Appreciate it. Thx
Off-grid w/ 2 Schneider XW Pro inverters & battery bank I plan to charge using 11kw generator. Installed everything. Inverter master-slave config working - powers house pulling from battery bank w/ factory pre-charge. Prob is can’t get Schneider AC2 input for generator to qualify to charge...
RCinFLA - from pix & comments you’re obviously knowledgeable...
Are you familiar w/ Schneider XW Pro AC2 issue of not qualifying? I have a small off-grid sys w/ 2 XW Pro inverters. I haven’t connected charge controllers. Too late in season.
My master-slave config works. My batter bank is...