Hello,
I am about to hook up my two solar arrays
PV Array1 44.3 VOC x 4 = 177.2 volts (In series)
PV Array2 39.9VOC x 10 = 399 volts (In series)
I called signature solar and they said each mppt can take 500 volts.
I see this in the spec sheet: Max PV Array Open Circuit 500VDC
I just want...
Hello,
Frist off I am very new to solar.
I have a small detached office that I would like to run using solar. Right now, I am running it from the grid. The most solar I could put on the roof would be about 800 watts. I am thinking of getting a Growatt 24V SPF 3000 and SOK 24V 100Ah LiFePO4...
Hello I am expecting my EG4 6500 EX tomorrow.
I am wondering if anyone sees any issues with the setup I want to do.
I would be using 1 EG4 6500 EX
AC input into the EG4 6500 EX from a 20-amp circuit from the main panel
AC output from the EG4 6500 EX to a load center/sub panel where it would...
I have one EG4 6500EX with a sticker that says 9/22. I have it setup to always be connected to the grid. I have the output going to a sub panel. At this point I am not sure if the way I set it up is correct/safe or not. I hope you cover how to set these up depending on the manufacture date.
I have an new EG4 6500 and 6 new Canadian 315 watt solar panels in series mounted to Unistrut.
I noticed that I get shocked if I touch the frame and the rain drip cap. Pictures included. I also get a reading between 60 and 100 volts. I am not sure what the issue is. Anyone have any ideas?
Thank...