You were correct! I installed my spare panel, hit about 260 volts, and next thing we were charging, harvesting 1600 watts, and
hi five'n. Within a couple hours, we were up to about 51 volts.Thank you sollap for solving our problem. Although we have a LONG way to go, this brought a lot of...
Mine had a 60 amp breaker on the AC out. Same amperage as the breaker on the A/C in panel before the inverter.
It was set up by a certified Schneider guy who had done many installs. So I'm pretty confident in his choice of equipment.
The electrician on this job took a look at it today. He is...
11 in series per controller.
I don't recall the exact calculations, but the 11 panels was under the 600 VOC max on the CC using the cold weather multiplier
which was somewhere around 1.2. I think I figured down to about Zero F. Adding the 12th was still under VOC max if not using the...
I think I will reconfigure my Array cables to 11 panels per controller. The two panels will sit there as spares. I could connect them in the summer and disconnect them in the winter. That wouldn't be a big deal if I remembered to do it.
So I purchased another MPPT 80-600 which I plan to swap...
I'm running a Schneider 6448 (6.4k / 48v.) inverter. Two MPPT 600's. Batteries and Grid Tied (to sell back).
I had 22 of my new 400 watt panels working (11 to each controller). I've been seeing a high of 6.31Kw on the inverter at what I would call peak sun (around noon).
That as calculated...
Schneider 6848.
We had guy hit the AC lines from my inverter to the house with a mini excavator digging a trench for
french drains. It pretty much shredded the lines and there was an obvious short. The inverter shut down.
Opening the breaker panel on the solar equipment, it tripped the...
I have a spare at a container in the woods, but we cannot get there yet due to trees down.
I probably have one or two with shattered glass that aren't wadded up or with holes in them.
We will test those as the other member suggested and mount them.
Thanks for everyone's advise so far.
I have...
I wish I had got back to this generator issue back in this time frame, but with all the other prepping needing done, I figured I would get to it later.
Well later is upon us after being hit by a F3 Tornado.
So yesterday I rolled the generator back out. Re-attached my chord from the 220 on...
I have a pair of Schneider Electric MPPT 80 600 charge controllers. Each controller has 12 panels feeding it 3,880 watts. It's been working fine for about 6 years.
The only time my system has thrown a code is when I had an attempted burglary 3 years ago and they flipped the breakers from the...
I didn't see a screen like this in the SCP. Only one that I mention in my post from today down below. It only had one setting I could change from 0 to 48. Can you take a look at that post and see what you think?
My question is a little more of a what to expect, vs how to. So here is my story and the question(s).
I'm not wiring the generator to auto-start/stop at this time. All I'm interested in doing is being able to manually start the generator
and have it charge batteries/supply power when needed...
I'm at my office logged into my system via a web browser logging into Conext Combox. That's a snippet of the generator settings page.
The only thing my XW has ever displayed is the watts coming off the charge controllers. I suppose there is a setting to change it to display something else...
Hi Guys. 9:03 PM Wednesday night my farm was hit with a F3. I was able to salvage 5 of my 24 315w panels. I have repositioned to one end of the rack and have them wired in series on one of my two MPT600's. When I take a voltage reading on the individual panels, I get about 43v open circuit on...
Like the title says. I'm connecting a generator to my system and have some questions. My "solar guy" has gone AWOL. Anybody here pretty familiar with
doing so and can answer some basic questions on set-up what's normal operation?
Hi Guys. 9:03 PM Wednesday night my farm was hit with a F3. I was able to salvage 5 of my 24 315w panels. I have repositioned to one end of the rack and have them wired in series on one of my two MPT600's. When I take a voltage reading on the individual panels, I get about 43v open circuit on...
It's been over three months since I last posted. The insurance company is finally producing some money for solar. That's a long story in itself.
I need to replace the old panels with new.
I'm wanting to get back to 24 panels. Specs on previous panels are...
SW 340 XL V oc 47.6 V mpp 38.0...
I had a Schneider Electric certified guy pick all of my equipment. I just did the install and he looked the wiring over and did the initial
settings. I've never considered or knew cold temps would make a difference in production.
When I did the calculation I came up with 637 volts. So yes, I...
I think we are onto something here. Thanks in advance for your help.
My Generator is 10,000 watt.
Should I change all three of these to the same value? So if 10%, 14A.
No, the generator was not changing in pitch so there was no load.
I have insight. Strange thing is I can log into that with my email and password, but when I make a setting change, it requires the credentials
again to save them. I won't accept the same credentials I logged in with. I changed email address to admin, and same problem. So the only
changes I...
This sounds like the most likely problem. I'm about 10 volts shy of the Min 230. I'll get that spare panel connected today if I have to hoof it in to get it there.
That's kind of what I was thinking. I've heard the term overpaneling before. Do you think it's sending the excess to grid or is it,
as someone else said, shaving it off? I'm all about turning that meter backwards when I can.