**UPDATE**
I spoke to Current Connected tech support and they advised me to change the power from grid to generator input, and limit the amperage in the web monitor app. I tried this and it seems to be working. My inverters are capped at 10.5KW.
I understand where you're coming from. Basically I am limited to a 50A pedestal because I live in a RV park full time. My hope is to run the RV (utilizing up to 50A like normal) while also charging my car at full power (32A) with a possible combined load of 82A. With each inverter limited to...
It usually happens when charging the car between 20-32A while using the 1500W indoor fireplace. I tripped the breaker twice doing this until I reduced down to 10-15A and then the issue resolved.
My hope initially were to use bypass to power the rv and use battery power to dump power into my...
Hello everyone!
I have scoured the manual, this forum, as well as asked Signature Solar Tech support and I am still at a loss.
Background on my system:
- Two 6000XP in parallel supplying split phase.
- 4 48V EG4 Lifep04 batteries in parallel (20KWH) with bus bars.
- Battery share active and...