    EG4 Chargeverter Settings

    Just installed the EG4 Chargeverter. Should the V be set at the batteries Absorption voltage? I have Fullriver DC1150-2 Batteries wired together in a 48V System. The data sheet says the absorption voltage is 58.8V, Bulk 58.8V. and Float at 54.6V. I currently have the EG4 Chargverter set at...
  2. the5thjourney

    Using Chargverter as generator input for Sol-Ark 15K set up for Smart Load

    Just installed the EG4 Chargeverter. Should the V be set at the batteries Absorption voltage? I have Fullriver DC1150-2 Batteries wired together in a 48V System. The data sheet says the absorption voltage is 58.8V, Bulk 58.8V. and Float at 54.6V. I currently have the EG4 Chargverter set at...
  3. the5thjourney

    XW Pro 6848 and Generator Issues? - ER56 EEPROM Error (Strings Fail) - Voltage not equal

    UPDATE: After spending several hours on the phone with Schneider they are warranting both inverters. He thinks the inverters had signal interference from using the CAT5e communication cables which caused the EEPROM errors and said I need to upgrade to CAT7. I was using the CAT5e cables that...
  4. the5thjourney

    XW Pro 6848 and Generator Issues? - ER56 EEPROM Error (Strings Fail) - Voltage not equal

    Hello BentleyJ, Both the inverters when originally installed had the same firmware. Hope I don't have to factory reset and go through firmware updates again but we'll see.
  5. the5thjourney

    XW Pro 6848 and Generator Issues? - ER56 EEPROM Error (Strings Fail) - Voltage not equal

    Have been off grid with for the past three years using Schneider products. Fired up the generator for the first time this season and the XW Pro 6848 Inverter started acting strange. In the past it would only accept the running watts of the generator, around 4kw. This time it tried to pull...