I originally thought he accidentally put his reply in a code block. But after looking at it a second I recognized what he was doing, although I am familiar with some coding anyways. He has basically mapped where to put the fuses and what size. He included the legend to read it...
Just wanted to hello to everyone! Im building off the grid on our recently moved to, hopefully soon to be, homestead. Will probably be asking a lot of questions here in the next few weeks about battery configuration. Looking forward to learning as much as I can! So far, just reading through the...
So I have 6 of the eg4-ll 48v 100ah batteries with signature solars rack that will be connected to a growatt 12k inverter. I have been looking at the forums and I lack the confidence to decide the wire size and fuse/breaker to go with due to my concern of safety.
The inverter manual says that...
If I did, I probably shouldn't answer that lol! My close friend has a brewery though, so that's handy. We plan to start distribution of kegs here real soon actually ;)
To be clear, you are suggesting separate 150amp fuses between the batteries and the bus bar on the racks that are supplied with 4awg wire. Followed by 4/0 wire from the bus bar to the inverter with a 400amp fuse, correct?
These batteries individually have 125amp breakers built into them. Are...