Recent content by Trygves

  1. Trygves

    I need some help with my Schneider System

    All well - the system was approved by the power company today. Thanks everyone for helping me. I sure educated myself a lot with this Schneider system.
  2. Trygves

    I need some help with my Schneider System

    Solved - the half-moon circuit breaker was in the wrong position and provided power to the house directly.
  3. Trygves

    I need some help with my Schneider System

    That must be the problem - the Association set-up. It currently shows all the correct names but those names are greyed out and I am not allowed to change or add them as I could when they were valid. At one time they were normal text and I could change them but now when t´hey are gray in color -...
  4. Trygves

    I need some help with my Schneider System

    That is the way I have it - GVS on and GFS off with Periodic Transmit Enabled. Still don't see home power on the display = why?
  5. Trygves

    I need some help with my Schneider System

    I am selling fine so the power goes towards the AC1 and is 0.7 kW in the picture above. But why no power to the house and all lights and TV is on.
  6. Trygves

    I need some help with my Schneider System

    What happened to my display as it will not show the house usage any longer? Anyone knows a quick fix to this - the SCP also do not show any power to the house although I get it at approx 1 kW.
  7. Trygves

    I need some help with my Schneider System

    I do not have the question mark so I can't educate myself. The other adjustments are...
  8. Trygves

    I need some help with my Schneider System

    The ACTIVE POWER CONTROL has the GFS, which I don't know what it means - it is Disabled in my system. The GRID VOLTAGE SUPPORT has the GVS button and it is Enabled in my system. Please let me know what others have them set at?
  9. Trygves

    I need some help with my Schneider System

    Under ACTIVE POWER CONTROL I have GFS Enable or Disable. What does GFS stand for and it is Disabled in my system - is that correct?
  10. Trygves

    I need some help with my Schneider System

    I appreciate all the help I have received here. Thank you all for contributing. What I learned - the Schneider has 2 firmwares 2.07.00 for the XW+6848 and I happened to use the wrong version first so all I got was 240 Volt from the unit and not 120 Volt times two. That destroyed a couple of...
  11. Trygves

    I need some help with my Schneider System

    I just changed to your values and now it seems to work ok = I have a green LED. What is strange is that if will not qualify if the Frequency is 59 - 61 Hz so it has to be wider to work. Very strange but reality - thanks my friends for helping me.
  12. Trygves

    I need some help with my Schneider System

    Almost the same as you... but tighter frequency requirements which should not matter I think.
  13. Trygves

    I need some help with my Schneider System

    Here is mine now with a dart LED
  14. Trygves

    I need some help with my Schneider System

    Anyone with a working system (I have XW+6848) please tell me if the green LED on the Inverter showing incoming AC1 is green or not lit at all even if full solar is available and the unit runs on solar. My LED is off = AC is present but not within qualifying range it tells me above.
  15. Trygves

    I need some help with my Schneider System

    Thank you hwy17 - that helps. Now the system is running ok but only on solar as the green LED which should qualify AC1 is not lit. That was my problem before all this started. So why don't I have a green LED light? Any ideas welcome at this time.