So I am going to check “Disable Float Charge”
The battery is not connected to a BMS port on inverter and installer said it has one built in. Here is the picture of full setup and battery.
Hello,
I recently got a 8KW Hybrid Solar System installed at my home. The company who installed the system have set the setting, which I am not sure if they are correct.
I am using 580w x 18 Jinko Bifacial Panles, with 8KW Inverex Nitrox Hybrid Inverter and a Lithium Battery ESM-48100B1.
I have...
Here are the current setting as per your recommendation. Thank you.
The installer set the equalization days to 90. I have now changed it to 0.
I need help with setting the correct ‘ Micro Inv input’ values
What it does is to allow battery to be used by ACs from ON volts till OFF volts and...
I have another question, most of the the day I don’t have load shedding and battery is full at 100%, I read keeping lithium artery at 100% is not recommended, so how can I limit the full charge at 90%
I have made the following changes. Thank you so much for such details and help.
Also there is a setting which the installer said that I need to adjust as per my requirements to use the battery for ACs.
It’s as Micro INV input values.
Which I want to use so when there is no grid or solar I can...